Okay lets use 30 gpm
With our aptly named Badger Meter at 1" there will be 2.5psi pressure loss at the meter.
http://www.badgermeter.com/getdoc/96...d-t-1-pdf.aspx
3/4" Badger meter the max they will measure it for is 25gpm to only have 2.5psi pressure loss would have one around 15gpm.
http://www.badgermeter.com/getdoc/2b..._8x4_4-BZ.aspx

Regardless though boots is correct that the 1" copper service is the limiting factor since 15gpm is the max one can use without exceeding 5fps
http://www.irrigationtutorials.com/copperloss.htm
Reply With Quote
  #32  
Old 07-18-2012, 11:07 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,694
Quote:
Originally Posted by FIMCO-MEISTER View Post
I've got tired head boots so I'll do my math in the morning but let's say we have 100' of 1" copper before the meter. PVB for back flow. Use the ops 70psi static. What is the max zone size with a 5/8 meter and what is the max zone size 1" meter. Forget the surcharge for now.
With modern 5/8~3/4 meters (the loss curve below is from a Badger 5/8~3/4 meter) there isn't any advantage gained by a switch to a one-inch meter, when there's a long run of copper upstream. The copper is the limiting factor, especially if you are going to pay attention to water velocity.
Attached Images
   
Reply With Quote
  #33  
Old 07-18-2012, 11:47 AM
FIMCO-MEISTER's Avatar
FIMCO-MEISTER FIMCO-MEISTER is offline
LawnSite Fanatic
 
Join Date: May 2007
Location: Red State America
Posts: 18,734
Did I not agree with you in my last post? Did I not acknowledge the rightness of your mind? Do I need to grovel?

Having said that I've seen some big increases in flow from swapping street meters. Especially if its one of those true 5/8 meters with the s copper on each side of it.
Reply With Quote
  #34  
Old 07-18-2012, 12:13 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,694
Quote:
Originally Posted by FIMCO-MEISTER View Post
Did I not agree with you in my last post? Did I not acknowledge the rightness of your mind? Do I need to grovel?

Having said that I've seen some big increases in flow from swapping street meters. Especially if its one of those true 5/8 meters with the s copper on each side of it.
no groveling required - I never saw your post - I was working on making images from charts
Reply With Quote
  #35  
Old 07-18-2012, 11:12 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,861
This is an interesting topic so what is the max zone size for each meter?
Posted via Mobile Device
Reply With Quote
  #36  
Old 07-19-2012, 07:18 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,694
I saw enough 20 gpm systems fed from true 5/8 meters to know the meters can run at max speed and no worries
Reply With Quote
  #37  
Old 07-19-2012, 02:02 PM
ls3c6 ls3c6 is offline
LawnSite Member
 
Join Date: Sep 2010
Location: Midwest
Posts: 78
system is being installed as we speak, i suppose if i run each zone and it doesn't send water HEAD TO HEAD then i complain, until then we can only speculate
Reply With Quote
  #38  
Old 07-19-2012, 03:28 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,694
Quote:
Originally Posted by ls3c6 View Post
system is being installed as we speak, i suppose if i run each zone and it doesn't send water HEAD TO HEAD then i complain, until then we can only speculate
you call city hall and order them to raise the water pressure
Reply With Quote
  #39  
Old 07-19-2012, 05:08 PM
AI Inc's Avatar
AI Inc AI Inc is offline
LawnSite Fanatic
 
Join Date: Dec 2007
Location: Southern NH
Posts: 21,391
Or take a walk downstairs and see if there is a PRV, if so , turn it up.
__________________
Reply With Quote
  #40  
Old 07-19-2012, 07:22 PM
bx24 bx24 is offline
LawnSite Senior Member
 
Join Date: Jun 2008
Location: MA/TX
Posts: 498
Quote:
Originally Posted by ls3c6 View Post
system is being installed as we speak, i suppose if i run each zone and it doesn't send water HEAD TO HEAD then i complain, until then we can only speculate
That is why I install heads 5 ft under max throw when I measure max PSI..I could do 33 easy but do 25 ft. Well worth it..Heads are cheap and keep customer happy.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 12:34 AM.

Page generated in 0.08382 seconds with 10 queries