Controller Troubleshooting - HELP!!!

Girlfriend's sprinkler system wasn't working. Contractor examined and said the controller (Imperial Valet) was bad. Quoted her a stiff price to replace it and no details about which controller, etc. and no other troubleshooting. Also said vacuum valve needed to be replaced. Suspected a rip-off.

I went online to determine best controller replacement for old Imperial Valet unit. Found a thread that a Hunter ICC was big enough to handle the supposed high current draw from old Imperial Valet Valves. Purchased and installed a new Hunter ICC controller. G/f called in a second contractor to replace the vacuum valve. Contractor installed valve and system still did not work.

Second contractor suspected that the new controller did not have enough output to turn on the master valve and zone valve. He wanted to either replace the master valve or remove it altogether. He thiought this might solve the ouput( current) problem. I was skeptical and suspected that the MV solenoid was defective.

I removed the old solenoid and sure enough the plunger was stuck/corroded. Ordered and installed a replacement solenoid and ran system manually through eight stations (Station 8 disconnected) . System worked perfectly! One set of wires (Station 8) remaining to be connected - connected them and re-ran manually and then nothing on all stations individually or in sequence!

Re-checked all connections for tightness
Disconnected station 8 Wiring
Cleared and re-set controller programming
Checked t/f output voltage at all station terminals - OK (24 vac)
removed and re-installed solenoid - nothing
re-check solenid resistance - OK
master valve bleed opening is clear
purchased an installed second solenoid and tried w/ 2 different plungers - nothing

Would appreciate some suggestions!!! feel like I'm re-inventing the wheel here - doesn't seem like there is anything left to check!!!


Ray





I purchased and installed a Hunter ICC controller to replace an Imperial Valet (out of business) controller with a bad transformer
Reply With Quote
  #2  
Old 10-11-2007, 02:04 PM
irrig8r irrig8r is offline
LawnSite Platinum Member
 
Join Date: Dec 2004
Location: Silicon Valley, CA
Posts: 4,545
I'd probably want to start with checking connections on the common wire. Any splices along the wires other than at the valves and clock?
__________________
Landscaper. Irrigator. Illuminator. Music lover. Coffee drinker.
Reply With Quote
  #3  
Old 10-11-2007, 02:12 PM
raya raya is offline
LawnSite Member
 
Join Date: Oct 2007
Location: Bedminster, NJ
Posts: 2
Gregg,

I found a splice on what appears to be the station 8 wire but this was disconnected. System worked fine once only and nothing else outside or underground was touched except the above-mentioned wire which again I believe is Station 8 and is disconnected?

Can you elaborate on the test you're referring to - VOM test on resistance in each circuit?

Ray
Reply With Quote
  #4  
Old 10-11-2007, 06:37 PM
Mike Leary's Avatar
Mike Leary Mike Leary is offline
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Cactus Hug, Arizona
Posts: 20,574
With the bleeder open on the mstr. valve will it fire? I'm thinking two
problems: solenoid and/or wiring at # 8 & solenoid and/or wiring at m.v.
Solenoids have been known to work, then after heating up ,fail. Are you sure
you have water? Sounds dumb, but you had to shut down when solenoids were changed. VOM should give you 15-50 ohms at the solenoid. With those
valves, I'm not sure of the inrush when two fire at once, but you should have
seen a fault on the clock. Water..power..vacation.
Reply With Quote
  #5  
Old 10-11-2007, 10:29 PM
irrig8r irrig8r is offline
LawnSite Platinum Member
 
Join Date: Dec 2004
Location: Silicon Valley, CA
Posts: 4,545
Can you elaborate on the test you're referring to - VOM test on resistance in each circuit?

Ray


Well, what I meant was pretty simple. By check I meant a visual check of the splices. Are they waterproofed? Could there be one that's corroded or loose?
__________________
Landscaper. Irrigator. Illuminator. Music lover. Coffee drinker.
Reply With Quote
  #6  
Old 10-11-2007, 11:04 PM
EagleLandscape's Avatar
EagleLandscape EagleLandscape is offline
LawnSite Platinum Member
 
Join Date: Aug 2003
Location: Garland, Texas
Posts: 4,325
You can always run new wires above the ground to the valve, run a common and a zone wire and lay them on top of the ground to see if that will solve it. If it fires up then, you know you have bad wire underground somewhere.

there are other ways to eliminate this option, ohm test, amp and volt test, but this is the simplist.
__________________
John Wingfield Jr.
Eagle Landscape and Irrigation
www.eagle-landscape.com
www.eagle-irrigation.com

"We are what we repeatedly do. Excellence, therefore, is not an act, but a habit." - Aristotle
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 12:03 PM.

Page generated in 0.07767 seconds with 7 queries