Quote:
Originally Posted by pete scalia View Post
You can't believe that your investigation was anywhere thorough . To make such a claim that no one has ever been seriously injured by less than 30 volts is ludicrous based upon your peripheral investigation. 15 volts was not just plucked from the air by UL. I have seen case after case where higher than 15v transformers dessimate lamps powered by higher volt taps. Not everyone changes a bulb immediately after it blows like they should. it's a domino effect and it's not pretty. even halogens don't last long when operating over 12 volts. Set aside safety and that alone is a real problem
Pete, do you really think 15v to a lamp wont burn them out just as quick. Fact is if you are using a 22v tap you probably are hundreds of feet away and need it. It would be no difference if you were closer and need a 15v. That argument is weak, stick with the fact that 16,17,18,19.........30v is so much more dangerous than 14, and 15. The fact that lamps burn out has nothing to do with the higher taps as much as it does with an increase when you lose a lamp. 13, 14, and 15 v are capable of overloading a lamp just as 22v can.

Its all in how you test and wire your system. An unliscensed contractor or homeowner should not be wiring our systems. We build them for the professional that should know what happens when you touch 2 sides of the cable togeather and also what happens when you stick your tounge on a frozen metal pole.

But hey if you dont need 15v then more power to you, I have said it before and I will say it again, we make a UL1838 TF, we just dont sell many of them.

Joey D.
Reply With Quote
  #82  
Old 12-18-2007, 11:23 PM
pete scalia pete scalia is offline
LawnSite Senior Member
 
Join Date: Sep 2007
Location: Long Island, New York
Posts: 960
Joey as much as I love you the higher voltage tap argument is not weak. When you have 11.8 volts at your homerun and you lose a 35 watt lamp you are in trouble on a long distant run with a higher than 15v tap. You are going to lose those other lamps very soon if you don't change that burnout immediately. Lamps were made to operate at 12v . They don't last very long at 12.5v and higher.
Reply With Quote
  #83  
Old 12-18-2007, 11:28 PM
JoeyD's Avatar
JoeyD JoeyD is offline
LawnSite Silver Member
 
Join Date: Aug 2007
Location: Escondido, CA
Posts: 2,965
Pete the chain reaction can and does happen when hooked up to taps 15v and below. Its all relative. If you are putting 12v on a run using a higher voltage tap you are going to increase the 12v no matter if its the 14 or 16v tap feeding it. This is just part of LV lighting. This is not a strong argument, do I have to break out the test equipment again?
Reply With Quote
  #84  
Old 12-18-2007, 11:36 PM
pete scalia pete scalia is offline
LawnSite Senior Member
 
Join Date: Sep 2007
Location: Long Island, New York
Posts: 960
Quote:
Originally Posted by JoeyD View Post
Pete the chain reaction can and does happen when hooked up to taps 15v and below. Its all relative. If you are putting 12v on a run using a higher voltage tap you are going to increase the 12v no matter if its the 14 or 16v tap feeding it. This is just part of LV lighting. This is not a strong argument, do I have to break out the test equipment again?
It doesn't take an electrical engineer.
The voltage drop from lamp load is greater than the loss of voltage due to resistance in cable
So if you are far out and get a burn out I'd rather be on a 15V tap than higher. The higher the tap in this instance the higher the voltage and the sooner the lamp will die.
Reply With Quote
  #85  
Old 12-18-2007, 11:41 PM
JoeyD's Avatar
JoeyD JoeyD is offline
LawnSite Silver Member
 
Join Date: Aug 2007
Location: Escondido, CA
Posts: 2,965
Quit avioding the fact that your 15 tap can create the same exact problem. That doesnt take an electrical engineer.

I will test it, and then let you know the results.
Reply With Quote
  #86  
Old 12-18-2007, 11:46 PM
pete scalia pete scalia is offline
LawnSite Senior Member
 
Join Date: Sep 2007
Location: Long Island, New York
Posts: 960
The higher the tap the higher the voltage.
Reply With Quote
  #87  
Old 12-19-2007, 10:42 AM
nate mullen nate mullen is offline
LawnSite Member
 
Join Date: Aug 2007
Location: escondido, ca.
Posts: 47
Quote:
Originally Posted by pete scalia View Post
Joey as much as I love you the higher voltage tap argument is not weak. When you have 11.8 volts at your homerun and you lose a 35 watt lamp you are in trouble on a long distant run with a higher than 15v tap. You are going to lose those other lamps very soon if you don't change that burnout immediately. Lamps were made to operate at 12v . They don't last very long at 12.5v and higher.

Pete, hey Buddy I'm a big fan and I am happy to set the record strait on this topic today and I will be setting the record straight on the NEC, UL 1838, 506, 1571, 1593, 2108, and the non existent 5058, as well as Voltage Drop..

I have sat back for my whole lighting career and watched how the industry has evolved and has ceased to evolve. There is no identity to this lighting industry. We as contractors sit here and have been taught by who? Yourself, a book that you cannot understand because you have no foundation, a manufacturer that has never installed a lighting job in their life...............I'm just about ready to get side tracked so back on point.

Increased Voltage to Lamps Above 12

FACT: you have 2 light bulbs @ about 100ft and you are using the 15v tap. This means you have a 3 volt drop shared between 2 fixtures, 1.5v per lamp. When one lamp burns out the other lamp will have 13.5v. At 13.5v the lamp life is dramatically reduced from 100% to 21% life which is 855 hours. If you had 15 volts at the lamp your life at the lamp is reduced to 5% of lamp life 215 hours. Above 15 volt.................what does it matter,.............fact is anything above 12 volts kills the lamp life.

THERE IS NO DIFFERENCE BETWEEN 13.14.15.16.17.18.19.20.OR 22 IT IS EXPONENTIAL EVEN AT 12.5 VOLTS THE LAMP LIFE IS 59% OF RATED LIFE. This is where it all gets back to proper wiring design.( more on this later)

So your right the higher the voltage the faster the lamp burns out. whether it burns out within 1 month or anything less it just does not matter.

I just have to say this, it is the NEC that is mandated across the US (and almost every other country), it is the bible when it comes to electricity NOT UL! Article 411 states 30v or less not 15. There is no need to discuss this further although I know it is going to be (please find me one job that has been turned down in the US, 10's of thousands of inspectors cant be wrong). If any of you wish to discuss this further I am more than willing to pay for a conference call and discuss this with great dialog.


To A Brighter future,
Nate
Reply With Quote
  #88  
Old 12-19-2007, 09:02 PM
pete scalia pete scalia is offline
LawnSite Senior Member
 
Join Date: Sep 2007
Location: Long Island, New York
Posts: 960
Quote:
Originally Posted by nate mullen View Post
Pete, hey Buddy I'm a big fan and I am happy to set the record strait on this topic today and I will be setting the record straight on the NEC, UL 1838, 506, 1571, 1593, 2108, and the non existent 5058, as well as Voltage Drop..

I have sat back for my whole lighting career and watched how the industry has evolved and has ceased to evolve. There is no identity to this lighting industry. We as contractors sit here and have been taught by who? Yourself, a book that you cannot understand because you have no foundation, a manufacturer that has never installed a lighting job in their life...............I'm just about ready to get side tracked so back on point.

Increased Voltage to Lamps Above 12

FACT: you have 2 light bulbs @ about 100ft and you are using the 15v tap. This means you have a 3 volt drop shared between 2 fixtures, 1.5v per lamp. When one lamp burns out the other lamp will have 13.5v. At 13.5v the lamp life is dramatically reduced from 100% to 21% life which is 855 hours. If you had 15 volts at the lamp your life at the lamp is reduced to 5% of lamp life 215 hours. Above 15 volt.................what does it matter,.............fact is anything above 12 volts kills the lamp life.

THERE IS NO DIFFERENCE BETWEEN 13.14.15.16.17.18.19.20.OR 22 IT IS EXPONENTIAL EVEN AT 12.5 VOLTS THE LAMP LIFE IS 59% OF RATED LIFE. This is where it all gets back to proper wiring design.( more on this later)

So your right the higher the voltage the faster the lamp burns out. whether it burns out within 1 month or anything less it just does not matter.

I just have to say this, it is the NEC that is mandated across the US (and almost every other country), it is the bible when it comes to electricity NOT UL! Article 411 states 30v or less not 15. There is no need to discuss this further although I know it is going to be (please find me one job that has been turned down in the US, 10's of thousands of inspectors cant be wrong). If any of you wish to discuss this further I am more than willing to pay for a conference call and discuss this with great dialog.


To A Brighter future,
Nate
Finally a fan. You see you numbskulls Nate Mullen knows class when he sees it. I'm a huge fan of you too Mr. Mullen. Can I call you Nate?
Reply With Quote
  #89  
Old 12-22-2007, 02:04 AM
johnh's Avatar
johnh johnh is offline
LawnSite Member
 
Join Date: Nov 2007
Location: Toronto, ON
Posts: 34
Quote:
Originally Posted by nate mullen View Post
Pete, hey Buddy I'm a big fan and I am happy to set the record strait on this topic today and I will be setting the record straight on the NEC, UL 1838, 506, 1571, 1593, 2108, and the non existent 5058, as well as Voltage Drop..
[JohnH]How about we let the authority set the record STRAIGHT? I have posed the question(s) to UL, the NFPA, and the IAEI, let's see what their responses are. And by the way, UL 5058 may not exist, but 5085(Joey transposed some numbers from a previous post) very much does exist. It is the binational code that your outdated now superseded CSA standard conforms to.
I have sat back for my whole lighting career and watched how the industry has evolved and has ceased to evolve. There is no identity to this lighting industry. We as contractors sit here and have been taught by who? Yourself, a book that you cannot understand because you have no foundation, a manufacturer that has never installed a lighting job in their life...............I'm just about ready to get side tracked so back on point.

Increased Voltage to Lamps Above 12

FACT: you have 2 light bulbs @ about 100ft and you are using the 15v tap. This means you have a 3 volt drop shared between 2 fixtures, 1.5v per lamp. When one lamp burns out the other lamp will have 13.5v. At 13.5v the lamp life is dramatically reduced from 100% to 21% life which is 855 hours. If you had 15 volts at the lamp your life at the lamp is reduced to 5% of lamp life 215 hours. Above 15 volt.................what does it matter,.............fact is anything above 12 volts kills the lamp life.

THERE IS NO DIFFERENCE BETWEEN 13.14.15.16.17.18.19.20.OR 22 IT IS EXPONENTIAL EVEN AT 12.5 VOLTS THE LAMP LIFE IS 59% OF RATED LIFE. This is where it all gets back to proper wiring design.( more on this later)
[JohnH]Except that there is a significant difference in the amount of heat generated from a 12V lamp operating at 15V and one operating at 22V.
So your right the higher the voltage the faster the lamp burns out. whether it burns out within 1 month or anything less it just does not matter.

I just have to say this, it is the NEC that is mandated across the US (and almost every other country), it is the bible when it comes to electricity NOT UL! Article 411 states 30v or less not 15. [JohnH] If the UL is so inconsequential, why do your transformers not say "conforms to NEC Article 411", why bother listing them at all, and labelling them as conforming to UL Standards?There is no need to discuss this further although I know it is going to be (please find me one job that has been turned down in the US, 10's of thousands of inspectors cant be wrong). If any of you wish to discuss this further I am more than willing to pay for a conference call and discuss this with great dialog.


To A Brighter future,
Nate
We may have a different hierarchy here in Canada, the CSA who develops the standards and provides the testing (others like UL, ETL, CE are also acceptable, as long as they are to Canadian standards) also writes the CEC (equivalent to NEC). Then there are the local authorities that enforce the code. But the CSA standards and the CEC are closely tied together, one referring to the other.
Do the NEC and UL not have a similar symbiotic relationship?
JH
Reply With Quote
  #90  
Old 12-23-2007, 11:00 AM
nate mullen nate mullen is offline
LawnSite Member
 
Join Date: Aug 2007
Location: escondido, ca.
Posts: 47
Quote:
Originally Posted by johnh View Post
We may have a different hierarchy here in Canada, the CSA who develops the standards and provides the testing (others like UL, ETL, CE are also acceptable, as long as they are to Canadian standards) also writes the CEC (equivalent to NEC). Then there are the local authorities that enforce the code. But the CSA standards and the CEC are closely tied together, one referring to the other.
Do the NEC and UL not have a similar symbiotic relationship?
JH
If the jobs are being inspected they need to be listed by a NRTL. at my last count there were 14 including ETL and UL. UL is a great company but all they do is wright standards. Then they come up with tests to meet those standards. 1838 was intended for lighting kits with every single conponate being tested and sold together, the wire, lamps, connectors,fixtures. With the expect ion of Malibu kits I know of nobldy that does this. I'm still waiting for some one to tell me why 120 volt lighting is OK .....if 1838 is the rule at 15 volts...by the way does't Kitchler, Nightscaping, Hadco, Vista and most other sell 120 volt lighting...........So back to UL standards there are many standards: under 15 volts, under 30 volts. over 30 volts to 120 volt's or higher. But make no mistake in the USA it is the NEC that stated what is legal or not legal. I really don't care .....I make all transformer's to comply with all listing for all standards for all uses.
To a Brighter Future.
Nate
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 04:08 PM.

Page generated in 0.12402 seconds with 8 queries