20V Solenoid?

I have a wire that is evidently nicked under a 40 ft drive. The controller is sending out ~25V but I am only getting ~20V at the valve. These are Irritrol Valves. I can't get the solenoid to fire. Are there any solenoids that will fire with less than 24V?
Reply With Quote
  #2  
Old 07-29-2008, 07:20 PM
CAPT Stream Rotar's Avatar
CAPT Stream Rotar CAPT Stream Rotar is offline
LawnSite Fanatic
 
Join Date: Apr 2007
Location: Cape Cod, Ma
Posts: 5,456
Battery operated valves.
Reply With Quote
  #3  
Old 07-29-2008, 07:20 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is offline
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,694
Any solenoid can fire with less than 20 volts, but you have to either fix the wiring fault or move on, as if it was completely cut.
Reply With Quote
  #4  
Old 07-29-2008, 10:08 PM
evergreensolutions evergreensolutions is offline
LawnSite Member
 
Join Date: Mar 2008
Location: Dallas, TX
Posts: 55
I purchased an IBOC, but would rather it operate from the controller. Cutting the concrete is not an option for this HOA.
Reply With Quote
  #5  
Old 07-29-2008, 10:16 PM
WalkGood WalkGood is offline
LawnSite Bronze Member
 
Join Date: Jun 2006
Location: Long Island, NY
Posts: 1,912
Quote:
Originally Posted by evergreensolutions View Post
I have a wire that is evidently nicked under a 40 ft drive. The controller is sending out ~25V but I am only getting ~20V at the valve. These are Irritrol Valves. I can't get the solenoid to fire. Are there any solenoids that will fire with less than 24V?
Hopefully this wire is in a sleeve under the drive? And you have no spare wires in there? Dig up the wire BEFORE the drive and test the voltage. Make sure you make a water-proof connection. Pinpoint the "bad" area of wire and replace it.
Reply With Quote
  #6  
Old 07-29-2008, 10:21 PM
EagleLandscape's Avatar
EagleLandscape EagleLandscape is offline
LawnSite Platinum Member
 
Join Date: Aug 2003
Location: Garland, Texas
Posts: 4,340
If it is an HOA< you will probably have a sleeve (PVC pipe conduit) under the driveway in which you can dig up both ends, and just snake a new wire through.

Best fix, not very expensive at all.

I would do that.
__________________
John Wingfield Jr.
Eagle Landscape and Irrigation
www.eagle-landscape.com
www.eagle-irrigation.com

"We are what we repeatedly do. Excellence, therefore, is not an act, but a habit." - Aristotle
Reply With Quote
  #7  
Old 07-29-2008, 10:25 PM
irrig8r irrig8r is offline
LawnSite Platinum Member
 
Join Date: Dec 2004
Location: Silicon Valley, CA
Posts: 4,545
I bet it's nice to be young and an optimist.....
__________________
Landscaper. Irrigator. Illuminator. Music lover. Coffee drinker.
Reply With Quote
  #8  
Old 07-29-2008, 10:47 PM
Waterit's Avatar
Waterit Waterit is offline
LawnSite Silver Member
 
Join Date: May 2008
Location: NW Florida
Posts: 2,735
Quote:
Originally Posted by irrig8r View Post
I bet it's nice to be young and an optimist.....
He's getting married Saturday - optimism defined!

JW - been married 17 years, honeymoon still ain't over!
__________________
BK
Reply With Quote
  #9  
Old 08-01-2008, 06:16 PM
WalkGood WalkGood is offline
LawnSite Bronze Member
 
Join Date: Jun 2006
Location: Long Island, NY
Posts: 1,912
Quote:
Originally Posted by jwingfield2k View Post
If it is an HOA< you will probably have a sleeve (PVC pipe conduit) under the driveway in which you can dig up both ends, and just snake a new wire through.

Best fix, not very expensive at all.

I would do that.

The voltage drop might not be caused by something at either immediate end of the drive. But I'd test the one end closest to the controller before digging the other side.
Reply With Quote
  #10  
Old 08-01-2008, 06:21 PM
Mike Leary's Avatar
Mike Leary Mike Leary is offline
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Port Angeles, Washington
Posts: 20,572
Quote:
Originally Posted by jwingfield2k View Post
If it is an HOA< you will probably have a sleeve (PVC pipe conduit) under the driveway
Hilarious comment of the month.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 07:01 AM.

Page generated in 0.09520 seconds with 7 queries