Quote:
Originally Posted by Venturewest View Post
Okay I tested it and here are the results:
I had a transformer set up in the front yard so this was easy. I used 16 gauge because I had a bunch right there, and one 50 Watt fixture to make the test simple and accurate.

So 60' distance to a 50 Watt Fixture, Output at transformer: 12.08 V

Voltage at fixture: 10.35 V and 3.89 Amps Vd=1.73

Complete loop, now 120' of wire, looping back to same terminals on transformer. Again verified 12.08 at terminal lugs.

Voltage at fixture: 11.22 V and same Amps. Vd=.86

I also checked my Amps through only one of the 16 gauge wires, and the Amperage was 1/2 of the 3.89 because the same amount of total Amps had twice as much wire to run through.
Am I missing something?
Lets see....I really like antique brass.

Ok here are the readings for the 2 tests that I promised to get. Now we have 3 tests done by me and one test by Venture - above - for VD in Loop Runs.

Please note that my last fixture on Circuit 3 is a medium base 50W in a light post...so I had to take the bulb out to take the readings....so the loads shown under circuit 3 already excluded this 50 W load ONLY when taking the 2 voltage readings at that fixture. I put that light bulb back to take all other readings shown in this table. (i.e. Circuit 3 bak-up to 275W for Test 1 and 235W for Test 2)

For circuit 2 the last fixture has 20W MR16....so I was able to get the readings at the pins without taking the light bulb out.

In summary; as I said earlier it seems the explanation of the resulting low VD Looping 12/2, which seems to equate single 8/2 wires, is that 12/2 cable has 65 strands of cooper and 8/2 cable has 133 strands of cooper...so looping 12/2 is actually using 2x65 = 130 strand of cooper which is almost the same - if not exactly the same - as using single 8/2 wires with 133 strand of cooper to that same load.
Attached Images
File Type: pdf VISTA - MT900.pdf (10.2 KB, 21 views)
Reply With Quote
  #142  
Old 02-24-2009, 06:41 PM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
awfully quiet...I guess no more criticism left for this DYI's ???
Reply With Quote
  #143  
Old 02-28-2009, 10:09 AM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
Quote:
Originally Posted by jimmy1111 View Post
Ok here are the readings for the 2 tests that I promised to get. Now we have 3 tests done by me and one test by Venture - above - for VD in Loop Runs.

Please note that my last fixture on Circuit 3 is a medium base 50W in a light post...so I had to take the bulb out to take the readings....so the loads shown under circuit 3 already excluded this 50 W load ONLY when taking the 2 voltage readings at that fixture. I put that light bulb back to take all other readings shown in this table. (i.e. Circuit 3 back to 275W for Test 1 and 235W for Test 2)

For circuit 2 the last fixture has 20W MR16....so I was able to get the readings at the pins without taking the light bulb out.

In summary; as I said earlier it seems the explanation of the resulting low VD Looping 12/2, which seems to equate single 8/2 wires, is that 12/2 cable has 65 strands of cooper and 8/2 cable has 133 strands of cooper...so looping 12/2 is actually using 2x65 = 130 strand of cooper which is almost the same - if not exactly the same - as using single 8/2 wires with 133 strand of cooper to that same load.

Here is another version of the 2 test readings in .jpg for those who can't read a .pdf file.

Again the point of the Loop run is NOT to run 2 cables in the same trench to a fixture but to pick-up some light fixtures on one leg out of the Transformer then some other light fixtures on the second leg back to the Transformer specially when the location of the light fixtures resemble to a circular or oval shape.

This is instead of running 2 single runs of lower gage cable (i.e. 8AWG instead of 12 AWG which is more $$$) to these 2 sets of fixtures and stopping short of connecting the last 2 fixtures (i.e. 10 or 15 ft of 12 AWG) together to make a Loop.
Attached Images
 
Reply With Quote
  #144  
Old 03-13-2009, 07:12 AM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
I guess I graduated !!!
Reply With Quote
  #145  
Old 03-13-2009, 11:05 AM
TXNSLighting's Avatar
TXNSLighting TXNSLighting is offline
LawnSite Fanatic
 
Join Date: Feb 2007
Location: DFW, TX
Posts: 6,460
yeh thats it...
__________________
Ryan

Always a lesson, never a failure.

www.meangreenlawncare.com
Reply With Quote
  #146  
Old 03-13-2009, 09:00 PM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
yay!!!...

You are invited to the Loop Runs Graduation Party ......eventhough I know what you did to this thread
Reply With Quote
  #147  
Old 03-15-2009, 01:33 PM
Go Halogen Go Halogen is offline
LawnSite Member
 
Join Date: May 2007
Location: bear delaware
Posts: 102
What has happened to this forum??

Insanity.....I have not been here for a while and I see that the forum still attracts too many weekend warriors that are trying to save a buck.

Jimmy, where did you come from? You need proper education.
Also, you took advantage of that Philly distributor. You are lucky that he took back your old transformer....once you mess with product the warranty is void.

Crazy stuff.....

- Andy (Go Halogen)
Reply With Quote
  #148  
Old 03-17-2009, 07:41 AM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
Quote:
Originally Posted by Go Halogen View Post
Insanity.....I have not been here for a while and I see that the forum still attracts too many weekend warriors that are trying to save a buck.

Jimmy, where did you come from? You need proper education.
Also, you took advantage of that Philly distributor. You are lucky that he took back your old transformer....once you mess with product the warranty is void.

Crazy stuff.....

- Andy (Go Halogen)
Well...the 12 AWG wire that i found fried inside is truly caused by Manufacturer defects for 2 reasons:
1. Like everyone said here bad conections have created the fire hazard condition inside the Trans....that is a safety issue that the Manufacturer avoided a law suit by replacing my Trans....eventhough I had to pay the $100 to the distributor.

2. 12AWG wire should never been installed inside the Trans. for each of the 300W ciurcuits when they are protected by 25 amp breakers. In this case the 12AWG wire which is rated at 20 amp was protecting the breaker and not the other way arround where it should have been. 10AWG which is rated at 30 amp should have been installed not the 12 AWG.

As soon as I said the above 2 fatal flaws to the Manufacturer they got stunned and offer me the replacement. Maybe that's why they have discontinued the older Model.

As far as proper eduction....thanks for some of the guys here.
Reply With Quote
  #149  
Old 04-07-2009, 07:12 AM
jimmy1111 jimmy1111 is offline
LawnSite Member
 
Join Date: Jan 2009
Location: philadlephia, pa
Posts: 56
i'm glad that i didn't go with spider web the runs all over the yard using hubs. I just got an irrigation system installed. not one run got hit.
Reply With Quote
Reply

Tags
landscape lighting , transformer , vista

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 08:26 PM.

Page generated in 0.11247 seconds with 8 queries