Other than using a chart - is there a way to determine if power wire to pump is too small?
Reply With Quote
  #12  
Old 09-04-2010, 06:56 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,052
Too small? For 8 amps you don't have much to worry about.
Reply With Quote
  #13  
Old 09-04-2010, 07:14 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,359
Quote:
Originally Posted by irg8ric View Post
Other than using a chart - is there a way to determine if power wire to pump is too small?
yes, but how far are you talking about? if the pump was installed by a well contractor the wiring should be suffecient to accomondate the length +20%

how old is the pump and is the controller sitting in southern exposure/full sun?

http://www.southwire.com/commercial/calculators.htm

this calculator is as handy as a shirt pocket. to get the length of the wire i'd use my TDR but you can measure or step off the estimated distance
Reply With Quote
  #14  
Old 09-04-2010, 07:20 PM
irg8ric irg8ric is offline
LawnSite Member
 
Join Date: Aug 2010
Location: Richmond, VA
Posts: 29
First off, thank you for the input.

I am assuming the reason the pump kicks on and then kicks off is the overload protection. Below are my thoughts on the matter - please reply.

This can be caused by: too small of wire, low/high voltage, or high ambient temp. After reading more about pumps - I am leaning towards a wiring issue - or maybe the overload protection on the pump is faulty.

Wire size is ok - #10 with app. 400'. however - the #10UF is plugged into a outlet - as opposed to being direct wired to the circuit.

Also, the relay adds a splice and there is a splice at the pump. In addition, the controller (rainbird esp modular) is powered by taking a leg of the 240v from the hot side of the psr.

I would like to rule out the possibility of this problem being caused by wire size (or too many splices) Can this be done?

Also, is there a way to determine if the overload protection on the pump is good?
Reply With Quote
  #15  
Old 09-04-2010, 07:57 PM
irg8ric irg8ric is offline
LawnSite Member
 
Join Date: Aug 2010
Location: Richmond, VA
Posts: 29
pump was installed 2003. controller is not in full sun
Reply With Quote
  #16  
Old 09-04-2010, 08:04 PM
bcg bcg is offline
LawnSite Bronze Member
 
Join Date: Mar 2005
Location: Tx
Posts: 1,714
Is this a new problem? Lets start with the basics, is there a pressure switch that's cutting it off? If not, sounds like you might have an oversensitive thermal overload protection relay or the pump is actually getting hot.
Reply With Quote
  #17  
Old 09-04-2010, 08:05 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,359
Quote:
Originally Posted by irg8ric View Post
First off, thank you for the input.

I am assuming the reason the pump kicks on and then kicks off is the overload protection. Below are my thoughts on the matter - please reply.

This can be caused by: too small of wire, low/high voltage, or high ambient temp. After reading more about pumps - I am leaning towards a wiring issue - or maybe the overload protection on the pump is faulty.

Wire size is ok - #10 with app. 400'. however - the #10UF is plugged into a outlet - as opposed to being direct wired to the circuit.

Also, the relay adds a splice and there is a splice at the pump. In addition, the controller (rainbird esp modular) is powered by taking a leg of the 240v from the hot side of the psr.

I would like to rule out the possibility of this problem being caused by wire size (or too many splices) Can this be done?

Also, is there a way to determine if the overload protection on the pump is good?
1 conductors per phase utilizing a #10 Copper conductor will limit the voltage drop to 2.87% or less when supplying 8.2 amps for 400 feet on a 240 volt system.
For Engineering Information Only:
30.0 Amps Rated ampacity of selected conductor
1.1417 Ohms Resistance (Ohms per 1000 feet)
0.05 Ohms Reactance (Ohms per 1000 feet)
7.199999999999999 volts maximum allowable voltage drop at 3%
6.884. Actual voltage drop loss at 2.87% for the circuit
0.9 Power Factor


you can get an electrican with a megger to troubleshoot for you, you can call the installer for input, you can take temperature readings with an ir thermometer.
to me 30 seconds is not long enough for the pump to get hot if it's in the water, the box on the other hand, may be in direct sunlight and the switches may have gotten hot and been damaged.
Reply With Quote
  #18  
Old 09-04-2010, 08:08 PM
irg8ric irg8ric is offline
LawnSite Member
 
Join Date: Aug 2010
Location: Richmond, VA
Posts: 29
no pressure switch
Reply With Quote
  #19  
Old 09-04-2010, 08:16 PM
Mike Leary's Avatar
Mike Leary Mike Leary is online now
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Alpine, Arizona
Posts: 20,496
Quote:
Originally Posted by 1idejim View Post
you can get an electrican with a megger to troubleshoot for you,
When I was at Maxi-Com school, the megger was considered a essential instrument to check and prove grounding. We just fried the electronics on a on-demand cistern system and I'm wondering why the breaker (220) did not trip before the smoke and smell.
Reply With Quote
  #20  
Old 09-04-2010, 08:27 PM
irg8ric irg8ric is offline
LawnSite Member
 
Join Date: Aug 2010
Location: Richmond, VA
Posts: 29
Quote:
Originally Posted by bcg View Post
Is this a new problem? Lets start with the basics, is there a pressure switch that's cutting it off? If not, sounds like you might have an oversensitive thermal overload protection relay or the pump is actually getting hot.
oversensitive overload protection - would this mean a new pump?
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 09:41 PM.

Page generated in 0.09478 seconds with 7 queries