#1
|
|||
|
|||
|
Transformer not rated for .....
Kichler transformer spec sheet says not rated for fixtures in water with humans..or something like that....
I need to put a couple LED Underwater lights into a waterfall that spills into a pool....i was always assuming it is safe, but why the disclaimer on transformer, and is it actually not safe?
__________________
|
|
#2
|
||||
|
||||
|
Hey Zohan,
Check this thread out, it might help you out. Also just do a search on Pool and Spa rated transformers and a ton of threads will come up with valuable information. Hope this helps Ken http://www.lawnsite.com/showthread.p...d+Transformers
__________________
Ken Martin ken@copperexpressions.com www.copperexpressions.com Member of LLI, AOLP, LO |
|
#3
|
|||
|
|||
|
Doesn't matter if the transformer is rated for. If your fixture isnt rated for human contact aka swimming pool then your fixture wont work. Im quality of putting 1 or 2 underwater lights in a koi pond on a standard transformer. But you wont find me using underwater lights in a waterfall for pool. Unless its a pentair or jandy or something pool rated..... Thats why we have fiber optics for pools
|
|
#4
|
|||
|
|||
|
should be spa and pool rated, but gotta tell you, seen tons of them installed by pool companies, and I am very unimpressed by the quality and feel of these "rated" trans. they look super cheap.
__________________
freedom |
|
#5
|
|||
|
|||
|
im confused....the lights are rated for underwater use so no problem there. Question is do i need a transformer that is rated for use with water fixtures that will be in a human contact area?
Worried about a safety issue... I will check the link too...thx
__________________
|
|
#6
|
|||
|
|||
|
Quote:
Transformers used to supply underwater luminaries must be listed as a swimming pool and spa transformer — and be of the isolating-winding type with a grounded metal barrier between the primary and secondary windings [680.23(A)(2)]. Branch circuits that supply underwater luminaries greater than 15V must be GFCI protected [680.23(A)(3)]. In 680.2, the NEC defines three general categories of underwater luminaries. Specifics, such as the wiring methods allowed to the forming shell and bonding requirements, are included for each type as follows: * Wet-niche [680.23(B)]. * Dry-niche [680.23(C)]. * No-niche [680.23(D)]. |
|
#7
|
||||
|
||||
|
Quote:
|
|
#8
|
|||
|
|||
|
Ok, great info guys thanks....
what I had planned on using (among other fixtures) was this http://www.landscapelighting.com/por...detail/15711SS and this http://www.landscapelighting.com/por...tail/15PR900SS but I guess thats a no go now. If I want to still do the pool waterfall I have 2 options 1. Put the fixtures along sides of waterfall instead of under the water 2. use a separate transformer rated for this
__________________
|
|
#9
|
|||
|
|||
|
There was a company that produced 12volt lighting fixtures for humnan contact. They are very expensive but try looking up nexxan or a company with a similar name. Pentair, jandy, hayward all make lights but most need to be in a niche. Not a free standing fixture.
Posted via Mobile Device |
|
#10
|
|||
|
|||
|
I haven't done any waterfall lights yet, so I ask you guys, if I put the lights right next to the stones where the water flows over will that look good at night or will it not work?