Quote:
Originally Posted by Wet_Boots View Post
That is not the remedy mentioned here. They installed a check in the line feeding the interior plumbing (keeping it from moving to the sprinkler supply when the zone is opened) and when you do that, the expansion tank is required.
My read on mitchgo's comment was that he is installing a check at the POC of the irrigation system so that the irrigation system would isolate the house line and irrigation line - like he said. I missed the part where he said that he was installing the check on the main feeding the house.

Quote:
Originally Posted by mitchgo View Post
Just wanted to let others know that after my own theory on this and ASI pretty much confirming my idea..

This works- Installing a check valve after the POC of the irrigation system to isolate the house line and irrigation line
Mick
Reply With Quote
  #22  
Old 09-09-2011, 12:36 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,498
I think that some of these situations might be worse nowadays, with water heater expansion tanks becoming commonplace, which easily makes for a monentary backflow from tank to POC when a zone is opened.
Reply With Quote
  #23  
Old 09-09-2011, 04:32 PM
AI Inc's Avatar
AI Inc AI Inc is online now
LawnSite Fanatic
 
Join Date: Dec 2007
Location: Southern NH
Posts: 21,206
Quote:
Originally Posted by Wet_Boots View Post
I think that some of these situations might be worse nowadays, with water heater expansion tanks becoming commonplace, which easily makes for a monentary backflow from tank to POC when a zone is opened.
You got that right. I dont think I ever had to deal with water hammer on a house that didnt have a expansion tank on the boiler.
__________________
Reply With Quote
  #24  
Old 09-11-2011, 08:29 PM
ASI's Avatar
ASI ASI is offline
LawnSite Member
 
Join Date: Apr 2009
Location: S.E. Indiana
Posts: 55
I am glad you were able to fix the problem. The check valve fix has always worked for me.
What kind of check valve did you use?

Quote:
Originally Posted by Kiril View Post
Mitch,

Thing is, you haven't solved the hammer problem, just masked it. Also, check valves aren't built to arrest water hammer .... expect premature failure.
__________________
Many of life's failures are people who did not realize how close they were to success when they gave up. Thomas A. Edison
Reply With Quote
  #25  
Old 09-11-2011, 08:58 PM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,318
What is so funny about what I said ASI? Both statements are 100% correct.
Reply With Quote
  #26  
Old 09-11-2011, 09:06 PM
Mike Leary's Avatar
Mike Leary Mike Leary is online now
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Port Angeles, Washington
Posts: 20,566
Quote:
Originally Posted by Kiril View Post
What is so funny about what I said?
Mom always said you had a rapier wit.
Reply With Quote
  #27  
Old 09-11-2011, 09:27 PM
mitchgo's Avatar
mitchgo mitchgo is offline
LawnSite Silver Member
 
Join Date: Dec 2008
Location: Redmond, WA
Posts: 2,620
Just a brass single way check valve


Kiril,

In every single situation other then this post I have seen with hammer noise coming around or from the PRV at the house which is typically right after SOV for the house. This still remains only when the system is turned on. Before I suggest anything I check to make sure All valves are fully opened

In these cases I've always recommend for the PRV to be replaced by a plumber and then to also have us install a Check Valve after the POC tee which is almost always at the water meter ranging typically 50-300' away. In my opinion I believe the PRV does like water flowing backwards through it and after years of it doing it it starts to fail the PRV.

In the situations I have dealt with. I have seen some systems with a couple irrigation valves cause the hammer noise to every valve cause the hammer. On the ones with every single valve- I went to the smallest zone and then turned off just about every single head to get a gpm of maybe 2-4 gpm.

Although it's less I still hear the hammer with the sudden inrush..

I'm sorry but a $2-300 basically for sure fix after the poc is a much more justifable thing to do then tell the customer oh.. Well now we have to install all sams, completely redesign the zone .. replace the pipe in order to fix this. For every zone.

I'll keep in mind and understand that it isn't the best solution , but it's a good quick fix. I do tell every customer that this may or may not work but i've had success in the past. The first 3 clients I offered to do it for free and then if it works charge half the normal charge.


Boots-

Of course I don't want to be screwing up anything inside the house

Can you explain on how installing a check valve after the point of connection for the irrigation system on the service line will affect the water heaters expansion tank? If it does have one or not? I'm no expert with them-

Last edited by mitchgo; 09-11-2011 at 09:31 PM.
Reply With Quote
  #28  
Old 09-11-2011, 09:51 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,498
Quote:
Originally Posted by mitchgo View Post
................Boots-

Of course I don't want to be screwing up anything inside the house

Can you explain on how installing a check valve after the point of connection for the irrigation system on the service line will affect the water heaters expansion tank? If it does have one or not? I'm no expert with them-
I don't think you made it clear that there was an expansion tank (or PRV) ~ the caution is for adding a check (or a PRV) without the heater getting an expansion tank at the same time. (although, most PRVs have an internal bypass to let excess downstream pressure bleed back through the device)
Reply With Quote
  #29  
Old 09-11-2011, 09:53 PM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,318
Mitch,

The point I am making here is, it is not a fix for the hammer. Just because you aren't hearing hammer anymore doesn't mean the hammer isn't still occurring .... i.e. you have masked the problem. If anything, you have made the downstream (of the CV) hammer worse. I think it is important that people understand this. Beyond that, unless the check valve is designed to handle shock loads (most aren't including the one ASI linked), they will fail prematurely.
Reply With Quote
  #30  
Old 09-16-2011, 06:55 PM
ASI's Avatar
ASI ASI is offline
LawnSite Member
 
Join Date: Apr 2009
Location: S.E. Indiana
Posts: 55
Mitch,
Any time you put a device that does not allow the flow of water back to the water main it is considered a closed loop. Installing a check valve, backflow, water meters with check valves or PVR in-between the main and the hot water heater will cause thermal expansion in the pipes. Closed loop and no tank you can expect the weakest link in your plumbing to let lose.

Kiril,
I thought you were kidding.
I believe there is a misunderstanding on the use of the check valve. I responded to Mitch post because I thought I could help. His description of what was happening was very close to what I have seen many times and the check valve had always worked. The first time I tried to correct the problem I wasted a lot of time by changing things and nothing worked. The check valve isolates the water in the house from irrigation system. There is no water hammer or stress on the check valve that would cause damage or failure. The check valve does what it is designed to do.It only allows the water to go one way.
__________________
Many of life's failures are people who did not realize how close they were to success when they gave up. Thomas A. Edison
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 05:22 PM.

Page generated in 0.10898 seconds with 7 queries