Valve Wiring Issue

Hey fellas i have 4 valves manifolded about 200 ft from the controller. None of them are working. I know its not the common because the valves on down the line are coming on fine. Do i have any other options other than running complete new wire to those 4 valves?
Reply With Quote
  #2  
Old 06-01-2011, 06:17 PM
hoskm01's Avatar
hoskm01 hoskm01 is offline
LawnSite Fanatic
 
Join Date: Aug 2005
Location: Phoenix Metro
Posts: 5,698
May be not the common (per se) but the connection to the common in the box?
__________________
Crayons taste like Purple
Reply With Quote
  #3  
Old 06-01-2011, 06:25 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,821
have you done electrical testing on the wiring?
Reply With Quote
  #4  
Old 06-01-2011, 07:40 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,895
Quote:
Originally Posted by Paris Landscaping Company View Post
Hey fellas i have 4 valves manifolded about 200 ft from the controller. None of them are working. I know its not the common because the valves on down the line are coming on fine. Do i have any other options other than running complete new wire to those 4 valves?
perform a short to earth measurement on the common and the valve wires. never rule out a common wire as it could be T-d in the field.
Reply With Quote
  #5  
Old 06-01-2011, 07:47 PM
Mike Leary's Avatar
Mike Leary Mike Leary is online now
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Winnemucca, Nevada
Posts: 20,579
Quote:
Originally Posted by 1idejim View Post
never rule out a common wire as it could be T-d in the field.
Words to live by. I've gone on calls of the same m.o. as the threadster and found a splice in a pit box, wiggled it, and the valves came on. Gosh, am I good!
Reply With Quote
  #6  
Old 06-01-2011, 11:54 PM
Paris Landscaping Company Paris Landscaping Company is offline
LawnSite Member
 
Join Date: May 2011
Location: Paris, TX
Posts: 28
Yea i have done some testing and i have 26V at the controller and all other valves except for these for 4 right in the middle of the yard. No clue where to go with this one. I dont wanna run those wires thru the yard but who knows i might have to. The electrical is terrible on this thing. Its only 3 years old and already has major problems the guy did water proof any connections.
Reply With Quote
  #7  
Old 06-02-2011, 12:40 AM
mitchgo's Avatar
mitchgo mitchgo is offline
LawnSite Silver Member
 
Join Date: Dec 2008
Location: Redmond, WA
Posts: 2,629
Trace backwards from the valve box to find your wire break
Reply With Quote
  #8  
Old 06-02-2011, 08:55 AM
hoskm01's Avatar
hoskm01 hoskm01 is offline
LawnSite Fanatic
 
Join Date: Aug 2005
Location: Phoenix Metro
Posts: 5,698
Quote:
Originally Posted by mitchgo View Post
Trace backwards from the valve box to find your wire break
Second'd..
__________________
Crayons taste like Purple
Reply With Quote
  #9  
Old 06-02-2011, 09:04 AM
FIMCO-MEISTER's Avatar
FIMCO-MEISTER FIMCO-MEISTER is offline
LawnSite Fanatic
 
Join Date: May 2007
Location: Red State America
Posts: 18,734
How would he TDR this Jim?
Reply With Quote
  #10  
Old 06-03-2011, 02:11 AM
Inspired's Avatar
Inspired Inspired is offline
LawnSite Senior Member
 
Join Date: Oct 2008
Location: Phoenix, AZ Zone 9
Posts: 540
Running new wire is for pussies.

Is the wire bundle a multi-conductor cable or a bunch of single wires?

I'll bet the common is "T"-d near the valves that don't work, or maybe in one of the boxes. 4 valves not working in one area sounds like a "common" problem to me.

Without a TDR and assuming you have ohm-d each station and have no continuity, I would disconnect the control wires at the manifold area (make sure you mark them with the station numbers first) and then using a jumper, ohm them all two at a time and identify the wire(s) with faults / bad connection(s).

Then starting at the valve box, hook the tracer (521) up to the faulted wire(s) and trace back toward the controller.
__________________
"Meeser Beell, The sprinkles not zackly, zackly, zackly." - Javier Larios
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 12:22 AM.

Page generated in 0.09706 seconds with 7 queries