I'm still not getting the idea of the icecube relay being at fault. It never sees the load of the motor, and it draws from a controller that would cut off its power if it were in any way an overload.
Reply With Quote
  #12  
Old 02-20-2012, 02:31 PM
jvanvliet's Avatar
jvanvliet jvanvliet is offline
LawnSite Gold Member
 
Join Date: Aug 2009
Location: South Florida
Posts: 3,935
Quote:
Originally Posted by Wet_Boots View Post
Anyway, I think the icecube relay would be incapable of tripping a pump's breaker, no matter what.
You're right; suspect the 24V transformer at this point, will post pictures this PM.
Reply With Quote
  #13  
Old 02-20-2012, 02:33 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,592
If you feed the pump relay directly with 24VAC, and leave the controller out of it, you may learn more. (assuming it is a relay with a 24VAC coil)
Reply With Quote
  #14  
Old 02-20-2012, 03:02 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 7,033
i think you may have eliminated the controller when you swapped it out for another, the transformer reads 26vac constant and the pump is working without the cube installed.

i wonder if the cube itself or the wiring to or from the cube is compatable as installed.

can you post a link to the PSR and the cube?
Reply With Quote
  #15  
Old 02-20-2012, 03:07 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,592
I don't see either a controller or a cube relay as even touching the 40-amp pump circuit. Apply power to the pump relay coil directly, and see if the pump keeps running.
Reply With Quote
  #16  
Old 02-20-2012, 04:29 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,592
TECO has a website, but "model 130674" doesn't scan. They have a DPA 2040 relay with a 7.5 HP rating for single-phase 240VAC
Reply With Quote
  #17  
Old 02-20-2012, 04:33 PM
jvanvliet's Avatar
jvanvliet jvanvliet is offline
LawnSite Gold Member
 
Join Date: Aug 2009
Location: South Florida
Posts: 3,935
Here's the problem; the controler is wired into the same 40 amp breaker as the motor

Draw on the Baldor is just over 36 amps +10% gets me to 39.6 max load, this combined with the controller is apparently enough to trip the breaker.

The pump station is in a remote location, pulling an additional line is too costly; I'm thinking of having the electrician replace the breaker with a 50 amp and setting the relay to trip @40 amps. Or I could suspect the breaker is bad and replace it with a new 40amp and pi$$ away some more time. The controler, well eh, they are cheap.
Reply With Quote
  #18  
Old 02-20-2012, 04:36 PM
jvanvliet's Avatar
jvanvliet jvanvliet is offline
LawnSite Gold Member
 
Join Date: Aug 2009
Location: South Florida
Posts: 3,935
Quote:
Originally Posted by Wet_Boots View Post
TECO has a website, but "model 130674" doesn't scan. They have a DPA 2040 relay with a 7.5 HP rating for single-phase 240VAC

I got the model # from Palm Beach Electric Motor who sold the unit. I've been busting a gut looking for some specs on it.

Was that TecoWestinghouse?
Reply With Quote
  #19  
Old 02-20-2012, 04:38 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,592
Does the controller have a choice of input voltage? Changing it to 240 from 120 would cut the current draw in half. You may not have the luxury of changing to a 50-amp breaker, depending on the wiring.

TECO is Chinese, so far as I can tell - it looks like you are running a motor that should have a higher ampacity circuit. Maybe someone bumped up from 5 HP
Reply With Quote
  #20  
Old 02-20-2012, 04:50 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,592
Here's the TECO DPA relays
Attached Images
 
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 02:31 PM.

Page generated in 0.09554 seconds with 8 queries