New electrical snafu for me.

I had to troubleshoot a non functioning valve yesterday. I had voltage at the solenoid but would not function. Installed another solenoid and still not operational. Same with a third. WTF??

I then put my meter in with the connections. As soon as I connected any of the solenoids, the voltage disappeared. I had only the common and the "hot" in the valve box. I was only a foot from where the cable left the building so I opened the cable and spliced in new wires to the box and all is well. The installer did not use waterproof wire nuts in the box so I think he used them underground as well. Nice guy that doofus.

I did not excavate in this situation but anticipate that in the future it will be needed as the remaining boxes are a long ways away.

John
Reply With Quote
  #2  
Old 06-01-2012, 08:15 AM
Sprinkus's Avatar
Sprinkus Sprinkus is offline
LawnSite Bronze Member
 
Join Date: Dec 2008
Location: San Antonio, TX
Posts: 1,800
Welcome to the wonderful world of troubleshooting poorly installed irrigation wiring.
Reply With Quote
  #3  
Old 06-01-2012, 08:38 AM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,832
Quote:
Originally Posted by jcom View Post
I had to troubleshoot a non functioning valve yesterday. I had voltage at the solenoid but would not function. Installed another solenoid and still not operational. Same with a third. WTF??

I then put my meter in with the connections. As soon as I connected any of the solenoids, the voltage disappeared. I had only the common and the "hot" in the valve box. I was only a foot from where the cable left the building so I opened the cable and spliced in new wires to the box and all is well. The installer did not use waterproof wire nuts in the box so I think he used them underground as well. Nice guy that doofus.

I did not excavate in this situation but anticipate that in the future it will be needed as the remaining boxes are a long ways away.

John
what were yovr restance measurements john. did you measure your short to earth and your vac potentials. what about amperage measurements. you have a situation that will be made easier if you can list and compare results
Posted via Mobile Device
Reply With Quote
  #4  
Old 06-01-2012, 08:59 AM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,318
Quote:
Originally Posted by jcom View Post
I had to troubleshoot a non functioning valve yesterday. I had voltage at the solenoid but would not function. Installed another solenoid and still not operational. Same with a third. WTF??
Just because you have the necessary voltage doesn't mean you have the necessary current. See the above post (Jim's).
Reply With Quote
  #5  
Old 06-01-2012, 12:45 PM
ArTurf ArTurf is online now
LawnSite Bronze Member
 
Join Date: Jan 2007
Location: Ark
Posts: 1,977
Quote:
Originally Posted by jcom View Post
I had to troubleshoot a non functioning valve yesterday. I had voltage at the solenoid but would not function. Installed another solenoid and still not operational. Same with a third. WTF??

I then put my meter in with the connections. As soon as I connected any of the solenoids, the voltage disappeared. I had only the common and the "hot" in the valve box. I was only a foot from where the cable left the building so I opened the cable and spliced in new wires to the box and all is well. The installer did not use waterproof wire nuts in the box so I think he used them underground as well. Nice guy that doofus.

I did not excavate in this situation but anticipate that in the future it will be needed as the remaining boxes are a long ways away.

John
Welcome to the world of ground faults and breaks. I got my feet wet on this last year on a golf course with 500 yard long runs of wire (talk about jumping straight into the frying pan). With the help of the good folks on this forum I was able to learn and somewhat conquer this. I actually don't run across this much in residential.
Reply With Quote
  #6  
Old 06-01-2012, 02:20 PM
jcom jcom is offline
LawnSite Senior Member
 
Join Date: Jan 2005
Location: Bismarck, ND
Posts: 791
This was my first time where the voltage would disappear when a load was hooked up. In the past, if I had voltage, the solenoid would operate.

I did not do any measurements as to common to ground, etc.. I expect more trouble in the future on this property. And I expect the problems to be the same.

Where the installer branched out to the individual boxes, he simply brought the hot and common to the box underground. Saved a few pennies by not bringing the cable into the box but instead just brought the individual conductors. I am sure he used non waterproof wire nuts underground to continue the common.

John
Reply With Quote
  #7  
Old 06-01-2012, 02:35 PM
Mike Leary's Avatar
Mike Leary Mike Leary is offline
LawnSite Fanatic
 
Join Date: Mar 2007
Location: Port Angeles, Washington
Posts: 20,567
Quote:
Originally Posted by jcom View Post
This was my first time where the voltage would disappear when a load was hooked up. In the past, if I had voltage, the solenoid would operate.

I did not do any measurements as to common to ground, etc.. I expect more trouble in the future on this property. And I expect the problems to be the same.

Where the installer branched out to the individual boxes, he simply brought the hot and common to the box underground. Saved a few pennies by not bringing the cable into the box but instead just brought the individual conductors. I am sure he used non waterproof wire nuts underground to continue the common.

John
I'm sure the client is overjoyed.
Reply With Quote
  #8  
Old 06-01-2012, 02:40 PM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,318
Quote:
Originally Posted by Mike Leary View Post
I'm sure the client is overjoyed.
I'm sure your old
Reply With Quote
  #9  
Old 06-01-2012, 04:31 PM
KrayzKajun's Avatar
KrayzKajun KrayzKajun is online now
LawnSite Fanatic
 
Join Date: Oct 2006
Location: Harvey,LA
Posts: 10,180
Quote:
Originally Posted by Sprinkus View Post
Welcome to the wonderful world of troubleshooting poorly installed irrigation wiring.
Amen to that!
Posted via Mobile Device
Reply With Quote
  #10  
Old 06-01-2012, 07:12 PM
agrostis agrostis is offline
LawnSite Bronze Member
 
Join Date: Nov 2009
Location: Winston-Salem NC
Posts: 1,658
You can find all kind's of problem's in all kind's of electrical thing's because of bad connection's all of the time.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 02:42 AM.

Page generated in 0.08385 seconds with 7 queries