Quote:
Originally Posted by DanaMac View Post
How are you figuring you are getting 25 psi at the heads with those nozzles? You have to take a field reading at the head to actually see what you are getting. It's going to take some time, and multiple nozzle change outs to get it right, or at least close. Are all the heads spaced at 47'? It's going to be a tough one. You might think about adding a head here or there, and moving some existing one, to get better spacing.

Are you putting 6 GPM nozzles on every head? No matter the area it is covering? This is a no-no. Let's say for instance you have a 1 GPM in a 90 degree corner. Then you should have a 2 in a 180 degree, a 3 in a 270 degree, and a 4 in a 360 degree. Matched precipitation.
I appreciate the help, thank you. I figure i am getting less than 25PSI at the head. I would like to know how to measure it at the head dynamically. I am only putting the 6GPM in the full circles, and i am using 3-4GPM in the 180s 1.5-2s at the 90s.
  #22  
Old 07-06-2012, 11:08 PM
DanaMac's Avatar
DanaMac DanaMac is offline
LawnSite Fanatic
 
Join Date: Mar 2002
Location: Somewhere in the state of CO
Posts: 13,049
Quote:
Originally Posted by turbosl2 View Post
I appreciate the help, thank you. I figure i am getting less than 25PSI at the head. I would like to know how to measure it at the head dynamically. I am only putting the 6GPM in the full circles, and i am using 3-4GPM in the 180s 1.5-2s at the 90s.
You must get a pitot tube and gauge. The tube goes in the direct spray of water directly in front of the nozzle. And you will get very wet
Here are some that are available Gauge and pitot tube
  #23  
Old 07-07-2012, 12:07 AM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,306
Quote:
Originally Posted by turbosl2 View Post
I measured it myself. I measured 12GPM at a 1/2" spigot right off my 3/4" meter. I also measured between 50-55PSI pressure, so i did start the design with the pressure and flow measurements , no way to design a system without it.
Would that be 50-55 PSI @ 12 GPM (eg. dynamic pressure) or your static pressure? Seems to me you probably designed around a static pressure and now you are having problems with coverage as your nozzle pressures are way below what you need.
  #24  
Old 07-07-2012, 12:12 AM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,306
Quote:
Originally Posted by turbosl2 View Post
I was told using hte .5" swing would help keep the pressure up.
That is pure bull.

Quote:
Originally Posted by turbosl2 View Post
I really do need the distance, i see for some reason the 3.0LA at 25PSI seems to throw more than i am getting now, and it only flows 3GPM but will lay down .51Inch of water using half the GPM, not sure how that is possible
If you don't have the pressure, renozzling is not going to get you the distance .... sorry. Also, your design is a little less than stellar on coverage, even if you did have the correct pressures.
  #25  
Old 07-07-2012, 08:40 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,833
The thing to do is to perform the flow and pressure tests simultaneously. Put the pressure gauge on your system blowout valve. Or better yet, on the backflow preventer. Open a zone, and read the pressure. Go to the water meter, and determine the flow. Pair those flow and pressure numbers together. Now close off the flow a bit, downstream of the pressure gauge and take a second set of flow-and-pressure numbers. Repeat the flow restricting, and take more flow-and-pressure measurements. You should end up with a table of paired flow-and-pressure numbers. That table is what your water supply really is. Your water supply is not a pressure. Your water supply is not a flow. It is a combination of flow and pressure, and that combination is what you design a system with.
  #26  
Old 07-07-2012, 08:50 AM
turbosl2 turbosl2 is offline
LawnSite Member
 
Join Date: Jul 2012
Location: Saratoga County, NY
Posts: 56
Quote:
Originally Posted by Wet_Boots View Post
The thing to do is to perform the flow and pressure tests simultaneously. Put the pressure gauge on your system blowout valve. Or better yet, on the backflow preventer. Open a zone, and read the pressure. Go to the water meter, and determine the flow. Pair those flow and pressure numbers together. Now close off the flow a bit, downstream of the pressure gauge and take a second set of flow-and-pressure numbers. Repeat the flow restricting, and take more flow-and-pressure measurements. You should end up with a table of paired flow-and-pressure numbers. That table is what your water supply really is. Your water supply is not a pressure. Your water supply is not a flow. It is a combination of flow and pressure, and that combination is what you design a system with.
I will try this, but will i still need the pressure at the head, or should it be equal inside at the backflow preventer and at the head. What do you think about using the 1/2 swing pipe, is that restricting me or helping me?
Posted via Mobile Device
  #27  
Old 07-07-2012, 09:16 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,833
What you need is one thing. What you actually have is another thing. Based on what you've described, you are plain and simple screwed.

Is the system entirely in place? Every single valve and head?
  #28  
Old 07-07-2012, 09:54 AM
turbosl2 turbosl2 is offline
LawnSite Member
 
Join Date: Jul 2012
Location: Saratoga County, NY
Posts: 56
Quote:
Originally Posted by Wet_Boots View Post
What you need is one thing. What you actually have is another thing. Based on what you've described, you are plain and simple screwed.

Is the system entirely in place? Every single valve and head?
That doesnt really say much. The system has been in place for 2yrs. I am just asking if the 1/2" swing pipe matters. I did some research and i dont think it does because my GPM is never going to exceed 6, and 1/2" or even 3/8" should flow 6GPM (1/2" pipe can flow about 14GPM) It not like the yard is not getting covered. I watched the system when it was all dirt, i was getting decent covereage. It could be that i am just not happy with the close in watering of the rainbird 5004 heads. With the pure sand the water goes right through it, and at the end of the stream i see green, but thats because substantial water falls there, so its not an even distribution.
  #29  
Old 07-07-2012, 10:29 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,833
The swing pipe only matters to the extent that it can subtract maybe one or two psi. Your system seems to be short by several dozen psi. You will never ever ever ever see any head on your system spray as far as 40 feet.
  #30  
Old 07-07-2012, 11:35 AM
FIMCO-MEISTER's Avatar
FIMCO-MEISTER FIMCO-MEISTER is offline
LawnSite Fanatic
 
Join Date: May 2007
Location: Red State America
Posts: 18,701
I doubt the funny pipe is the main issue like boots says something else is going on. I wouldn't use funny pipe trying to push 6gpm though. It is a bottleneck in a system that needs minimum pressure loss. 40' is really pushing it. 30-35' max with 5000s in my book. May have to swap them all out to maxi paws.
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 02:29 AM.

Page generated in 0.08470 seconds with 8 queries