Troubleshooting Toro question

Tried a search, but got too many possibilities, and I don't have much time to pore through all the threads... My apologies for a lame question - we do basic service on the few systems at our accounts, but sub out all installs and major repairs. Nursing home we care for is between facility managers, we can't get approval for diddly and the lawn is frying.
Installed ten years or so ago by good-sized irrigation company; Toro controller with the 8-dial zone/timers, and digital display, two zones, toro valves (I think - square grey bodies, 1x1 inch square tops).
If set to run manually at the controller either zone won't come on, but if you flip the little black auto/manual switch on the valve up and back down, they will come on, run the full time and shut off automatically. Is this normal behavior? Can we trust the system to come on at 3 a.m. (At the moment, I don't)
Reply With Quote
  #2  
Old 07-12-2012, 07:13 PM
Autoflow's Avatar
Autoflow Autoflow is offline
LawnSite Member
 
Join Date: Jun 2010
Location: Sydney, Australia
Posts: 245
It sounds like the system has a master valve that is working and the zone valves that are not working. When you turn the system on manual at the controller, the master valve turns on which lets the water go through the main and so the valves will run. Are you leaving the black switch (Weathermatic valve?) on? Is there enough pressure to run two zones at once?

Check the controller to see if there is a wire installed into the pump/MV port on the controller.
Reply With Quote
  #3  
Old 07-12-2012, 07:37 PM
Michdeere Michdeere is offline
LawnSite Member
 
Join Date: Nov 2005
Location: Michigan
Posts: 90
Sounds like Weathermatic valves. There were/are issues with the Weathermatic solenoids. Maybe you have solenoids that are not strong enough to pull the plunger up and open the valve. When you move that black lever, you're manually pushing the plunger up and the electromagnet then takes over and holds the valve open until the clock shuts it off. I'd be those suspicious of those solenoids. An ohm meter is your friend.
Reply With Quote
  #4  
Old 07-12-2012, 08:34 PM
lakesregionscapes lakesregionscapes is offline
LawnSite Member
 
Join Date: Mar 2006
Location: Tuftonboro,NH
Posts: 131
Thanks for the really quick replies - and the explanation makes a great deal of sense to me.
What should the ohms read? (I think we have a meter somewhere - I'm going digging)

The rest of the lawn is watered by 4 zones run by a newer Hunter controller from a different part of the building: when we blow out the whole place in fall, the compressor hooks up where the single water line (town water) comes out of the building (I think I remember a lever type shutoff just inside) and blows out all 6 zones. No idea if or where the master valve for the Toro section would be... But the two zones we are working on both work fine manually from the valves. Not enough pressure to run properly with both open at once, but fine one at a time, after we replaced two broken heads. This 2 zone area hasn't been run in 2 or 3 years, because someone from building maintenance didn't like a head spraying a walkway or something, so they ripped the power cord right out of the controller box. We couldn't get the OK to fix it then, but it rained enough to squeak through. Not this year.
Reply With Quote
  #5  
Old 07-12-2012, 08:47 PM
lakesregionscapes lakesregionscapes is offline
LawnSite Member
 
Join Date: Mar 2006
Location: Tuftonboro,NH
Posts: 131
Quote:
Originally Posted by Autoflow View Post
It sounds like the system has a master valve that is working and the zone valves that are not working. When you turn the system on manual at the controller, the master valve turns on which lets the water go through the main and so the valves will run. Are you leaving the black switch (Weathermatic valve?) on? Is there enough pressure to run two zones at once?

Check the controller to see if there is a wire installed into the pump/MV port on the controller.
I'll check the controller tomorrow for a MV wire. We were turning off the black switch once the valve was tripped, which was what made it so odd: manual control from the controller didn't work until you ran outside and flipped the switch up and back down - then it ran...
This system ran fine for several years, but I'm not surprised parts are starting to fail, it has been a while since it was put in.
Reply With Quote
  #6  
Old 07-12-2012, 08:51 PM
DanaMac's Avatar
DanaMac DanaMac is online now
LawnSite Fanatic
 
Join Date: Mar 2002
Location: Somewhere in the state of CO
Posts: 13,072
Those valves are most likely Weathermatic, not Toro.
Reply With Quote
  #7  
Old 07-12-2012, 09:08 PM
Michdeere Michdeere is offline
LawnSite Member
 
Join Date: Nov 2005
Location: Michigan
Posts: 90
[QUOTE=lakesregionscapes;4469274]
What should the ohms read? (I think we have a meter somewhere - I'm going digging)

Typical reading would be 20 to 50 ohms. I've seen as high as 65, but they don't last long...

I'm usually satisfied with 30-40 ohms.
Reply With Quote
  #8  
Old 07-12-2012, 10:04 PM
lakesregionscapes lakesregionscapes is offline
LawnSite Member
 
Join Date: Mar 2006
Location: Tuftonboro,NH
Posts: 131
Found the meter; tomorrow we'll test them, and be prepared to dig up and replace the pair of valves with something different, based on the inventory of our local parts dealer (mostly Hunter I suspect)... there is one Weathermatic in the other 4-zone section, and it drives us nuts - I think I'll be glad when that one craps out.
Thanks for all of the helpful info: it stinks having a property you maintain look bed because they're too cheap: make us look like hacks, and that's not right. We try to work around these issues when we can. Really appreciate the help.
Reply With Quote
  #9  
Old 07-16-2012, 07:39 AM
lakesregionscapes lakesregionscapes is offline
LawnSite Member
 
Join Date: Mar 2006
Location: Tuftonboro,NH
Posts: 131
Figured I'd follow up with our results... tested the valves (confirmed Weathermatics), and both read around 32 Ohms, which turned our attention back to the controller box. We happened to read the volts at the valve box and it was around 5V for the line that was off, and 10-11V on the one that was on. Saw the valves are 24V and thought those readings seemed awfully low. Couldn't see anything wrong in the controller box, so took the model number and hit the 'net for the manual. (Toro Vision ll Plus). At some point I realized we'd had two transformers hanging around, both for Toro boxes - one came off a replaced controller. Checked both, and though both were 24VAC, one was 16.25VA, the other much higher (not in front of me now). The model we have is supposed to use an even higher VA than that.
Called Toro technical service at 4:45 pm on Friday and left a message. They actually call back within an hour: I am now really impressed with them - didn't expect anything 'til Monday. He explaiedn that the controller is a two stage system; 12 or 15 volts for the panel, 24 volts for the valves... I'm sure this is all ABC's to you guys, but it was news to me
Armed with the correct (or less incorrect?) transformer, went back Saturday (4th trip in 3 days), and wired the transformer in correctly - it had been removed while we were gone so building maintenance didn't try to "help" and put set the system to run. We have water!
Not sure at this point if it was wired backwards, or the transformer output was too weak, or both, but we didn't have enough juice to open the solenoids, and now we do.
Thanks everyone for the help - not only does our system work, but I understand why, and we stopped looking at the wrong end of the problem. Plus we'll be better equipped for the next snag we encounter (hopefully)...
Reply With Quote
  #10  
Old 07-16-2012, 08:38 AM
DanaMac's Avatar
DanaMac DanaMac is online now
LawnSite Fanatic
 
Join Date: Mar 2002
Location: Somewhere in the state of CO
Posts: 13,072
Now is a good time to recommend replacing that controller. The Vision series have had many issues. Not many of us full time service people like them. Whenever I see a problem with one, I try to replace it. If there are no problems, I leave as is.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 04:57 AM.

Page generated in 0.06843 seconds with 7 queries