Service connection question

I have a 2" connection to make and the pressure is around 125. i'm gonna put in a regulator, but i'm trying to figure how to tie in after the meter. Its a prefab meter pit that only has room for the water meter.

So out of the meter, i'm gonna come up to the RP and regulator, but i'm wondering how to do it. normally i would use PVC, but i think it's best to use copper. Assuming a male or female fitting coming off the meter pit, i figure i'll need and adapter (M/F) and an el with a riser, then an el into the assembly. After that i'll switch to PVC.

My questions are, 1, assuming sweat fittings are not usable under ground, what do you recommend for the proper fittings? And 2, where to put the PRV, before or after the RPZ, assuming it will be an assembly? And 3, can you winterize through a PRV? i cant recall an instance where i ever did.

thanks for all your help.

pat
Reply With Quote
  #2  
Old 09-26-2012, 08:00 PM
greenmonster304's Avatar
greenmonster304 greenmonster304 is online now
LawnSite Silver Member
 
Join Date: Jul 2007
Location: You Know
Posts: 2,498
if the meter isn't set yet you could use 2" K copper in a "U" shape that would go from the meter pit to above grade where you could make your sweat connections. then there would only be the connection in the pit for the water authority to make .
Reply With Quote
  #3  
Old 09-26-2012, 08:01 PM
irritation's Avatar
irritation irritation is offline
LawnSite Silver Member
 
Join Date: Jul 2006
Location: Indianapolis, IN
Posts: 2,625
Copper looped up from meter pit to above ground location, set RP, copper down to PRV in valve box and go with PVC.
Reply With Quote
  #4  
Old 09-26-2012, 08:36 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,375
I haven't seen any problems with purveyors over sweat fittings below grade, as long as they're downstream of the meter.
Reply With Quote
  #5  
Old 09-26-2012, 08:53 PM
Without A Drought Without A Drought is offline
LawnSite Senior Member
 
Join Date: Jul 2006
Location: New Jersey
Posts: 850
its a pre-fab pit. the down pipe after the meter is pre installed. and done prior to us getting on site. i have to dig it up just to see what i have to work with
Reply With Quote
  #6  
Old 09-26-2012, 09:03 PM
irritation's Avatar
irritation irritation is offline
LawnSite Silver Member
 
Join Date: Jul 2006
Location: Indianapolis, IN
Posts: 2,625
I would rather drill out of the foundation than have a connection 3'-4' below grade. Sweat or compression. I have seen buried copper corrode near sweat connections.
Reply With Quote
  #7  
Old 09-26-2012, 09:07 PM
irritation's Avatar
irritation irritation is offline
LawnSite Silver Member
 
Join Date: Jul 2006
Location: Indianapolis, IN
Posts: 2,625
Quote:
Originally Posted by Without A Drought View Post
its a pre-fab pit. the down pipe after the meter is pre installed. and done prior to us getting on site. i have to dig it up just to see what i have to work with
Is this meter just for irrigation? If so replace the pipe.
Reply With Quote
  #8  
Old 09-26-2012, 09:26 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 40,375
2-inch meters are flanged, so you can just get another flange and gasket.
Reply With Quote
  #9  
Old 09-26-2012, 10:32 PM
the irrigator the irrigator is offline
LawnSite Member
 
Join Date: Dec 2007
Location: Long Island, NY
Posts: 59
Quote:
Originally Posted by Wet_Boots View Post
I haven't seen any problems with purveyors over sweat fittings below grade, as long as they're downstream of the meter.
Do sweat joints below grade meet code in NY ? I've always used compression.
Reply With Quote
  #10  
Old 09-26-2012, 10:55 PM
greenmonster304's Avatar
greenmonster304 greenmonster304 is online now
LawnSite Silver Member
 
Join Date: Jul 2007
Location: You Know
Posts: 2,498
Quote:
Originally Posted by the irrigator View Post
Do sweat joints below grade meet code in NY ? I've always used compression.
Plumbers I work with say compression only in suffolk county
Posted via Mobile Device
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 03:10 AM.

Page generated in 0.06901 seconds with 7 queries