Why 24vac won't actuate a solenoid

Quite a few times i see a post where the OP states that he has 24 volts but the solenoid won't work.

I always ask the same few questions, what is the resistance of the wire path and solenoid and what short to earth is.

I took a call from a friend in Texas this week, 24 vac, but he also had 180 ohms resistance from the controller.

Most troubleshooters will begin fooling with the splices because that's what we're taught.

Before i look at anything i will take a short to earth measurement to test the wire insulation. If the insulation is good i look at the splices, if the insulation is bad i grab the A-frame.

Most solenoids require 300mA - 500mA inrush to lift the plunger. That's 7 - 12vA.

Using Ohms law you can see why the valve won't open.

24vac/180ohms=0.133333mA.

There are 24vA in one Amp. 1A/24vac = 0.041667mA or 1vA.

0.133333/0.041667 = 3vA, less than half the current required to magnatize the coil and lift the plunger.

Electrical troubleshooting can be made a lot easier by doing a little more testing and a lot less guessing.

Hope this helps someone.
Posted via Mobile Device
Reply With Quote
  #2  
Old 01-27-2013, 11:29 AM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,209
Too many numbers .... brain is boiling .... can't reme
Reply With Quote
  #3  
Old 01-27-2013, 11:34 AM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,079
A current reading is the most helpful measurement. Aside from a leakage meter, what's a good clamp-on ammeter with a low range?
Reply With Quote
  #4  
Old 01-27-2013, 11:37 AM
Kiril Kiril is offline
LawnSite Fanatic
 
Join Date: Jun 2007
Location: District 9 CA
Posts: 18,209
Quote:
Originally Posted by Wet_Boots View Post
A current reading is the most helpful measurement. Aside from a leakage meter, what's a good clamp-on ammeter with a low range?
Too expensive, that what it is.
Reply With Quote
  #5  
Old 01-27-2013, 12:24 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,079
C'mon, techies, there has to be some sort of improvement in the state of the art

Reply With Quote
  #6  
Old 01-27-2013, 06:08 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,371
Quote:
Originally Posted by Wet_Boots View Post
C'mon, techies, there has to be some sort of improvement in the state of the art

I had one of those analog amperage testers Shoes, i will see if i didn't toss it. Sperry made some tough instruments.

Armada, greenlee, excell, fluke, all make good stuff.

Accurate measuring instruments are hard to find at Harbor Freight though.
Posted via Mobile Device
Reply With Quote
  #7  
Old 01-27-2013, 10:36 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,079
You have to wonder if all the technical ends of a multimeter haven't been condensed into a single chip by now, leaving only the quality of enclosure and switches as factors in determining the worth of these instruments.
Reply With Quote
  #8  
Old 01-28-2013, 01:08 AM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,371
Quote:
Originally Posted by Wet_Boots View Post
A current reading is the most helpful measurement. Aside from a leakage meter, what's a good clamp-on ammeter with a low range?
There are a number of inexpensive and yet reliable clamps out there that measure .000 Shoes.

Point of the thread is that for the tech that actually uses a multimeter, values can be measured or calculated close enough to make critical path decisions.

Line voltage / transformer output, voltage drop as well as resistance and current can be measured or calculated to an acceptible degree of accuracy. Close enough to make decisions rather than guesses.
Posted via Mobile Device
Reply With Quote
  #9  
Old 01-28-2013, 01:24 AM
cjohn2000's Avatar
cjohn2000 cjohn2000 is offline
LawnSite Senior Member
 
Join Date: Jun 2010
Location: Tacoma, WA
Posts: 414
Quote:
Originally Posted by Kiril View Post
Too many numbers .... brain is boiling .... can't reme
Doesn't help with someones upside down profile pic.
Reply With Quote
  #10  
Old 01-28-2013, 02:46 PM
irrig8r irrig8r is offline
LawnSite Platinum Member
 
Join Date: Dec 2004
Location: Silicon Valley, CA
Posts: 4,543
----------------------
__________________
Landscaper. Irrigator. Illuminator. Music lover. Coffee drinker.

Last edited by irrig8r; 01-28-2013 at 02:54 PM.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 11:02 PM.

Page generated in 0.08340 seconds with 9 queries