If say I do loose 15 lbs over the 400ft... and I have a static of 90psi at meter... I need a pressure reducer anyways but would u leave the pressure on the high side to compensate for the Loss at the end of the run... or u think I will have issues with water hammer and that jazz...
Posted via Mobile Device |
|
#22
|
||||
|
||||
|
Quote:
Last edited by Mike Leary; 02-24-2013 at 05:22 PM. |
|
#23
|
|||
|
|||
|
Yep.. do u prefer to upsize pipe to get more gpm and.more rotors on a zone or prefer small pipe (1") and just do less rotors? Or do smaller pipe with more rotors and.nozzle them down and have longer run times? The price difference between the two sizes 1.25 and 1 are pretty big around here... you get so muh more flow with the 1.25 though. I prefer less run times and put more water out quicker... soaking in the ground and runoff isn't an issue with this soil...
Posted via Mobile Device |
|
#24
|
||||
|
||||
|
On a large system, you upsize the mainline pipe first. From source to the greatest distance, the pressure loss should be less than 5 psi, in order for you to obtain uniform performance from zone to zone. Also, a long mainline run greatly magnifies the effects of water hammer, to the point where you can blow apart the zone valves at the end of the line.
|
|
#25
|
|||
|
|||
|
Well I will.have a master valve if a problem.ever does blow a mainline but I don't want that of course...the way this land is 150 wide 400 deep...there's not many options on how I can run this mainline to shorten it unless I want run my laterals longer which I don't think makes much sense either...
Posted via Mobile Device |
|
#26
|
||||
|
||||
|
Quote:
Water hammer is a function of water velocity and pipeline length. It doesn't take even a hundred feet of length to make for damaging hammer. Since you can't shorten the mainline length, you slow down the water velocity. Slow it way down. |
|
#27
|
||||
|
||||
|
You will never,ever, get more gpm than the service provides, nor will you get any more pressure. You design for what you got; then deduct for the friction loss and the demand of the zones, and, bingo, there's your system. Easy, we do it every day.
|
|
#28
|
|||
|
|||
|
Yes sir so service being 1" and looks like ill.need to slow it down so upsizing isn't an option... may even.need to go up to 1.5 in. Need to run. Velocity numbers to make.sure Im not over 5...
Posted via Mobile Device |
|
#29
|
||||
|
||||
|
With 90 psi street pressure, and 400 feet for the mainline, you want to forget about the usual velocity guidelines, and go even slower.
|
|
#30
|
||||
|
||||
|
IF is the question. PSI must be measured, as well as flow output. Anything less is lumpy gravy and guaranteed to fail.
|
![]() |