Interesting Find

Went on a job yesterday afternoon where the sprinklers wouldn't come on.

Well system so i verified water by bleeding a few valves.

Hydraulics eliminated i went to the controller. No response on manual single station.

118 vac in 28.2 out.

Continuity on all stations but no tone on 3 stations. Those 3 stations made my meter buzz or hum during the test.

I began to isolate the system and test each path a number of ways.

There were 8 stations in use, 1 & 2 were 14 ga single strand (one of which was stranded wire) with 14 ga common. 3 runs of 18 ga multi strand with only 2 commons in use.

Stations 1 = 25 ohms, 2 = 52 ohms.

I measured the number 1 common against the remaining stations to pair them up, here is what i got.

3-99, 4-27, 5-13, 6-25, 7-100, 8-100

Next i measured common 2 against all of those stations.

3=54, 4=18, 5=58, 6=71, 7=57, 8=58

When i left the system was working in both manual and in a test program that i set up.

This was a thought twister, what do you think i found?

My money is on Sprinkus, maybe Boots figuring this out in a hurry.


Posted via Mobile Device
Reply With Quote
  #2  
Old 07-01-2013, 02:48 PM
Wet_Boots's Avatar
Wet_Boots Wet_Boots is online now
LawnSite Fanatic
 
Join Date: Mar 2005
Location: metro NYC
Posts: 39,500
some bad parallel/series wiring juju going on there
Reply With Quote
  #3  
Old 07-01-2013, 03:31 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,826
Quote:
Originally Posted by Wet_Boots View Post
some bad parallel/series wiring juju going on there
Yup, knew you would figure it out. Now, best guess on where i found it?

Hint: i was onsite 1.5 hrs and only worked in 1 VB.

Where did i find the problem?


Posted via Mobile Device
Reply With Quote
  #4  
Old 07-01-2013, 05:15 PM
CAPT Stream Rotar's Avatar
CAPT Stream Rotar CAPT Stream Rotar is offline
LawnSite Fanatic
 
Join Date: Apr 2007
Location: Cape Cod, Ma
Posts: 5,441
short common/partial connection? located @ clock?
Reply With Quote
  #5  
Old 07-01-2013, 06:32 PM
bcg bcg is online now
LawnSite Bronze Member
 
Join Date: Mar 2005
Location: Tx
Posts: 1,769
My guess is the problem was with the wiring at the valve for zone 2 but I could completely wrong. I do much better with these when I can put my hands on the wires and troubleshoot them visually in addition to the meter.
Reply With Quote
  #6  
Old 07-01-2013, 10:35 PM
grassman177's Avatar
grassman177 grassman177 is offline
LawnSite Fanatic
 
Join Date: Oct 2007
Location: leavenworth, kansas
Posts: 9,786
i think at valve 2 as well, common. I found something like that recently, on a new system i installed. Had no common making it to valve one and mv, at the end of the wire.
__________________
all is fair in love and grass! Man, it smells like sheet, do you smell that!!
Reply With Quote
  #7  
Old 07-01-2013, 10:36 PM
jbell36 jbell36 is offline
LawnSite Bronze Member
 
Join Date: Feb 2008
Location: KANSAS
Posts: 1,214
subscribed...
Reply With Quote
  #8  
Old 07-01-2013, 11:41 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,826
Quote:
Originally Posted by jbell36 View Post
subscribed...
Don't just sit on the fence and wait for an answer, draw a number from the hat and give us your best shot. This is a learning moment for all of us.

Even though they don't speak up much, there are some top notch troubleshooter's on this forum (even Boots) and i would like to hear what they think.

I would like to let this ride for a couple days, that way maybe Sprink, BCG, Waterlogged, Dana, Hosk, Txirrigation, Irrigation Contractor, A1, Boots, irritation and ML will chime in too.

You lurkers toss out a theory, you might be right, you might not.

I just thought this was a little more of a challange than we usually see.

The numbers are there, take a shot.
Posted via Mobile Device
Reply With Quote
  #9  
Old 07-01-2013, 11:49 PM
jbell36 jbell36 is offline
LawnSite Bronze Member
 
Join Date: Feb 2008
Location: KANSAS
Posts: 1,214
ive only been doing irrigation for 2 years now, so i'm still learning a lot, especially when it comes to electrical...i learn a LOT from this site, and think threads like this one are the most helpful, we should do more of these more often...i've got one for you guys after this one gets cleared up...

my initial thought was zones 4, 5, and 6 were giving you trouble...i'll give this one some thought tomorrow morning and see what i can come up with...i'm still a little confused on the wiring coming into the controller tho
Reply With Quote
  #10  
Old 07-01-2013, 11:59 PM
mitchgo's Avatar
mitchgo mitchgo is offline
LawnSite Silver Member
 
Join Date: Dec 2008
Location: Redmond, WA
Posts: 2,620
hmmm

Common was in series with zones 4 and 5 ?
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 09:57 PM.

Page generated in 0.08515 seconds with 7 queries