  #1  
Old 08-14-2013, 07:24 PM
MEXANDME MEXANDME is offline
LawnSite Senior Member
 
Join Date: Apr 2004
Location: MYRTLE BEACH,SC
Posts: 395
Troubleshooting Zone Wire(s)

Last valve on the run, i.e., only the common and one zone wire gets to this valve.

Getting 16 volts to the valve so valve will not open.

Valve opens fine with valve activator.

27.3 volts leaving the clock.

Is the problem more likely to be in the common or the zone wire or is there anyway to tell?

The irrigation wires parallel the electrical wires feeding the house all the way to the valve so I am getting a lot of static from the electrical. I was able to find the valve but cannot distinguish where the fault may be.

Thanks,

Mex
Reply With Quote
  #2  
Old 08-14-2013, 07:43 PM
Cape Atlantic Landscaping's Avatar
Cape Atlantic Landscaping Cape Atlantic Landscaping is offline
LawnSite Member
 
Join Date: Mar 2011
Location: Cape May, New Jersey
Posts: 37
you need to do a resistance test (Ohms) at the controller you should see 20- 60 ohms
second go out to valve solenoid and ohm that out to the correct numbers above

my guess would be bad splice at solenoid wire connection to field wiring

cut and trim new ends and reconnect splice then check numbers again

to actuate a valve 24-27 volts is preferred

when trimming wires check for corrosion in wire itself, it should be clean like a new penny
__________________
Reply With Quote
  #3  
Old 08-14-2013, 07:50 PM
Cape Atlantic Landscaping's Avatar
Cape Atlantic Landscaping Cape Atlantic Landscaping is offline
LawnSite Member
 
Join Date: Mar 2011
Location: Cape May, New Jersey
Posts: 37
I should add when you test field wiring at controller its best to test wires with controller unplugged and battery out of controller or disconnect common and zone wire from panel
like I said before, bad splices are all to common. That is probably one of my biggest complaint's is crappy splices, interior wire nuts no grease, black tape and so on.
__________________
Reply With Quote
  #4  
Old 08-14-2013, 08:11 PM
Cape Atlantic Landscaping's Avatar
Cape Atlantic Landscaping Cape Atlantic Landscaping is offline
LawnSite Member
 
Join Date: Mar 2011
Location: Cape May, New Jersey
Posts: 37
how long of a run is it to controller ? if under lets say 50 ft. run a single wire out to valve from controller and hook up to solenoid one at a time. replacing one for the other and turn it on a see what happens.
that would tell you what wire is possible bad.
__________________
Reply With Quote
  #5  
Old 08-14-2013, 09:16 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,358
Quote:
Originally Posted by MEXANDME View Post
Last valve on the run, i.e., only the common and one zone wire gets to this valve.

Getting 16 volts to the valve so valve will not open.

Valve opens fine with valve activator.

27.3 volts leaving the clock.

Is the problem more likely to be in the common or the zone wire or is there anyway to tell?

The irrigation wires parallel the electrical wires feeding the house all the way to the valve so I am getting a lot of static from the electrical. I was able to find the valve but cannot distinguish where the fault may be.

Thanks,

Mex
Mex, you have another goober here.

This all depends on how you take your measurements.

I kinda make it a rule to check the common at the last working valve before getting too wound up.

If you didn't get lucky then go to the clock and take resistance measurements of all zones.

Next remove the first zone wire and measure the static voltage of the zone.

Put the zone wire back and measure voltage on it and all of the zones under load (dynamic).

If you have the ability to measure the current draws on all stations, do it and write all of these measurements down for future reference.

If your resistance measurement is 150 or above then you look at loose connections.

If the resistance is below 7 ohms look for a short.

To find ground faults, use a short to earth measurement. Greater than 700,000 ohms and you are ok, below 700,000 you have earth contact. Way below up to and including 0, you see the severity of the compromise.

When you took the in field voltage measurement did you exclude the common or did you measure the voltage to ground?

If the valve wire was measured to ground, look at the zone wire.

If the common was included you can confuse yourself Mex, read the simplest numbers.

I don't like to guess so i won't - you have my number anyhow. Call me if you need some help.
Reply With Quote
  #6  
Old 08-15-2013, 05:41 AM
CAPT Stream Rotar's Avatar
CAPT Stream Rotar CAPT Stream Rotar is offline
LawnSite Fanatic
 
Join Date: Apr 2007
Location: Cape Cod, Ma
Posts: 5,353
Is it multi strand or single strand?
as said before ohms.
STE- on both com and field wire.

good luck gotta love someone who doesn't quit! play on player.
Reply With Quote
  #7  
Old 08-16-2013, 07:58 AM
MEXANDME MEXANDME is offline
LawnSite Senior Member
 
Join Date: Apr 2004
Location: MYRTLE BEACH,SC
Posts: 395
All,

Thanks for your feedback/help!

We have had three days of solid rain here so I have not been back yet.

Homeowner lives out of town and will all the rain....no rush to get back.

I will keep you posted.

Regards,

Mex
Reply With Quote
  #8  
Old 08-21-2013, 11:30 AM
MEXANDME MEXANDME is offline
LawnSite Senior Member
 
Join Date: Apr 2004
Location: MYRTLE BEACH,SC
Posts: 395
All,

Thanks again for your help!

With the zone turned on at the clock, and the wires disconnected from the solenoid at the non-working valve, I read 16 volts across the zone wire and the common.

I read 21 volts across the zone wire and a ground probe. So, I assumed it was the common that was the problem.

I located the next working valve back toward the clock which was only 45 feet from the non-working valve. I laid out a temp common on the ground between the two locations and the valve then worked from the clock.

Since the existing wiring was in the same trench with the power and I was getting lots and lots of static from the power and the entire areas was full of 30-year old shrubs and trees, I "wimped out" and just replaced the last 45 feet of wire rather than trying to find/fix the fault.

Do I get an "F" or maybe just a "D-"?

Thanks again for your help!

Mex
Reply With Quote
  #9  
Old 08-21-2013, 09:27 PM
ArTurf ArTurf is offline
LawnSite Bronze Member
 
Join Date: Jan 2007
Location: Ark
Posts: 1,775
I'm not the expert Jim and some others are but I'll give you an b+. I think you understand the principles and it would be difficult to locate the compromise without a fault finder.
Reply With Quote
  #10  
Old 08-21-2013, 10:22 PM
1idejim's Avatar
1idejim 1idejim is online now
LawnSite Fanatic
 
Join Date: Jul 2009
Location: State of Jefferson
Posts: 6,358
It is working and that is what you were after. I would be wondering about a 6.3 vac loss if the system is ave residential size though.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump






Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ©1998 - 2012, LawnSite.comô - Moose River Media
All times are GMT -4. The time now is 03:48 PM.

Page generated in 0.08210 seconds with 7 queries