2" Pressure regulator

Discussion in 'Irrigation' started by Some Sprinkler Guy, Aug 18, 2010.

  1. Some Sprinkler Guy

    Some Sprinkler Guy LawnSite Member
    Posts: 167

    Does anyone have any recommendations on a 2" pressure regulator?

    Ive got some ball fields that are surging and blowing stuff apart. I want to be able to adjust above 75psi, but it looks like the BR-4 above 1-1/4" tops out at 75.
     
  2. Rotor_Tool

    Rotor_Tool LawnSite Senior Member
    Posts: 349

    If your system pressure doesn't exceed 100psi, have you considered using a master valve with a pressure regulator? Maybe a Rain Bird PGA or PEB valve with the PRS-D?

    Just a thought....
     
  3. Wet_Boots

    Wet_Boots LawnSite Fanatic
    Posts: 47,320

    There are also specialty valves that will only open partially, until a set pressure is reached downstream. The idea behind them is to restrict the flow until all the air has rushed out of the sprinkler heads. Big bucks payup
     
  4. CA Green

    CA Green LawnSite Member
    Posts: 80

    I agree with Rotor Tool, RB PEB should do the job.
    Posted via Mobile Device
     
  5. Sprinkus

    Sprinkus LawnSite Silver Member
    Posts: 2,099

    Sounds like a pressure sustaining valve.
     
  6. Wet_Boots

    Wet_Boots LawnSite Fanatic
    Posts: 47,320

    There might be an additional descriptor, but that's the general category they belong to. I had a client with a golf course that was always having heads blow off their connections, and I suggested he either go to these specialty valves, or parallel the zone valves with much smaller ones and open them first, to let the lines fill.
     
  7. Some Sprinkler Guy

    Some Sprinkler Guy LawnSite Member
    Posts: 167

    Its on a reclaimed water line. Pressure reads 125 but I suspect surges to 150ish. We can't keep the old lines together. Valves keep seeping too. Didn't want master valves because there are multiple field / controllers etc.
    Posted via Mobile Device
     
  8. Sprinkus

    Sprinkus LawnSite Silver Member
    Posts: 2,099

    GPM requirement?
    Mainline size?
    Length of mainline?
    If it's a big site then I would probably be looking at some sort of Bermad pressure reducing valve.
     