blown fuse

Discussion in 'Irrigation' started by Fishin LCO, May 31, 2004.

  1. Fishin LCO

    Fishin LCO LawnSite Member
    from NC
    Posts: 143

    I need a little help. I think these may be a simple solution I can fix if not I will tell my customer to see an irrigation specialist. Here is the problem. The control panel flashes PR Off, which I assumes means power off. I looked into it and found it was the fuse blown in the box I replaced it and ran the all the zones manually and it work fine. Well it happened again, so I replaced the fuse again. I worked again, but blew the fuse once again. I am thinking it blows the fuse when it cuts on automatically. Is this a bad connections somewhere, bad ground, bad relay or what? Thanks for any help.
     
  2. JeffY

    JeffY LawnSite Senior Member
    Posts: 324

    What kind of controller is this? Rainbird? Hunter? If it's Rainbird LX series, and the fuse is blowing whenever it wants to run a cycle, it's becasue of a faulty transformer. Get a replacement for it and it should take care of the problem.
     
  3. BSME

    BSME LawnSite Senior Member
    from Midwest
    Posts: 829

    One single solenoid or wire could be blowing the fuse... What I would do (may or may not be the most efficient method but works for me) replace the fuse.... go through the zones manually until the fuse blows... when you find out what zone is blowing the fuse find that valve in the valve box.... when you find that valve cut the wires going into the solenoid... if you replace the fuse and go through that zone again without the fuse blowing then it's the solenoid... replace the solenoid... this method will cost you either one or two fuses
     
  4. Planter

    Planter LawnSite Member
    from Utah
    Posts: 214

    Might not hurt to remove the common wire at the controller and check the resistance for each zone. I'll bet you'll find it. If they are fine use the multi tester to see what the AC is at the transformer, but I'll be its in the field wiring.
     
  5. Fishin LCO

    Fishin LCO LawnSite Member
    from NC
    Posts: 143

    BSME, you were right on the money. I really appreaciate the help. thank you everyone. yall are the best
     
  6. HBFOXJr

    HBFOXJr LawnSite Bronze Member
    Posts: 1,712

    BSME is right. However we occasionally find solinoids that ohm out normal but still don't work or work properly popping fuses. It is called an intermittent open. Same thing can happen in a car battery. simple volt test looks normal but won't crank. In both cases the electrical load causes a break down of continuity in some time frame of useage.

    A load tester will find the defective battery. In irrigation don't be afraid to swap the solinoid as in this case even though it ohms OK.
     