Hammer while flushing

Discussion in 'Irrigation' started by F6Hawk, Jul 7, 2005.

  1. F6Hawk

    F6Hawk LawnSite Member
    Posts: 195

    As I was flushing my zones last night, without the heads installed, I shut off the zone, and was shocked to experience some water hammer. Two or three bangs as the flow stopped. Is this normal without the heads providing some back pressure? Or do I have a serious problem on my hands here?

    To recap: 1-1/4" main (approx 200' from 3/4" meter to valves), with 1" lats, and 3/4" on the last head in each zone, 65 psi static. Please tell me this is acceptable without the back pressure of the heads!

  2. Wet_Boots

    Wet_Boots LawnSite Fanatic
    Posts: 47,712

    You can definitely get banging when zone valves open into an open pipe. You may also see it every spring when you first open the system, with the pipes being empty.
  3. F6Hawk

    F6Hawk LawnSite Member
    Posts: 195

    Thanks, WB, you nailed it, of course. Put some heads on those funny pipes, and no more hammer. 3 zones down, 4 more to go! Here's hopin' I can "get 'er done!" before Dennis hits us!