how do you bury your cable

Discussion in 'Landscape Lighting' started by TheHotShotKid, Mar 10, 2006.

  1. TheHotShotKid

    TheHotShotKid LawnSite Member
    from Ohio
    Posts: 169

    just wondering.
     
  2. sheshovel

    sheshovel LawnSite Fanatic
    Posts: 5,112

    I bury it under dirt in a shallow trench or dont bury it at all and put mulch over it..if it is to run under a walkway or pathway I run it thru ABS pipe and bury that.
     
  3. steveparrott

    steveparrott Sponsor
    Posts: 1,205

    Note article 300.5 of the NEC code regarding burial of low voltage wiring:

    -All locations not specified below: 6 inches
    -In trench below minimum 2" thick concrete: 6 inches
    -Under a building: In raceway only
    -Under roads, alleys, public driveways and parking lots: 24 inches
    -Under one- and two-family dwelling driveways and outdoor parking areas and used only for dwelling-related purposes: 18 inches
    -In or under airport runways, including adjacent areas where trespassing is prohibited: 18 inches
     
  4. NightScenes

    NightScenes LawnSite Silver Member
    Posts: 2,209

    There ya go Steve!!
     
  5. TheHotShotKid

    TheHotShotKid LawnSite Member
    from Ohio
    Posts: 169

    I guess I'm in violation then and should get back out to that airport and sink my cable a bit deeper under the runway so it complies.:laugh:
     
  6. niteliters

    niteliters LawnSite Senior Member
    Posts: 537

    i usually go 24" when going under aiport runways...can't be too safe.:)
     
  7. dcondon

    dcondon LawnSite Silver Member
    Posts: 2,246

    Make sure you go deep enough so the frost dosen't bring it to the surface in the spring. :waving:
     