Hunter/Buckner Genesis Controller

Discussion in 'Irrigation' started by ArTurf, Aug 20, 2011.

  1. ArTurf

    ArTurf LawnSite Gold Member
    Male, from Ark
    Posts: 3,338

    Has anyone ever worked with this controller? It is designed for Golf or large properties. I am dealing with 4 of these on a golf course. Recently the power stopped going through 2 of the controllers transformers, 120V in nothing out. This happened on almost the same day. The transformers have a reset button but it will not reset and doesn't appear to be tripped. These controllers are independent although they may share the same power supply. There were no storms or lightning strikes in the area lately. Any idea what may have went wrong with these? Is there anyway I can check the transformers to be sure they are good/bad? It is odd to me that the 2 went out at the same time.
     
  2. mitchgo

    mitchgo LawnSite Silver Member
    Posts: 2,758

    Can you get access to the transformers connection leading into the controller?
    If you can disconnect them from the controller and test for power to for the transformer only- if nothing go for a new one.
    If you do have power but no display then the controller has failed.