Running electric under a road

Discussion in 'Hardscaping' started by kootoomootoo, Mar 18, 2006.

  1. kootoomootoo

    kootoomootoo LawnSite Platinum Member
    Posts: 4,369

    Any of you guys know the requirements for running electric under a road out to an island. I am assuming it is 2in electrical conduit / 24 inches deep.
  2. dcondon

    dcondon LawnSite Silver Member
    Posts: 2,246

    We just had some put in and it had to be 3 inch conduit and 36 inches deep. Not sure if it's the same in your state. Hope this helps.
  3. Dirty Water

    Dirty Water LawnSite Fanatic
    Posts: 6,799

    It varies from state to state and county to county.

    What voltage?

    Over here anything after the meter needs to be 18" down if its in conduit, or 24" if its direct buried.

    If it is between the Meter and the Transformer, it needs to be 24" in conduit.

    Between the line and the transformer needs to be 38" in conduit.

    Since your running it out to a island, I'm assuming 110, Usually 18" in a conduit (Because its under a road :D ) will suffice.

    There is no code here for conduit size, most 110v and 220v feeds are 10 gauge or so and can be ran in 1" conduit.
  4. kootoomootoo

    kootoomootoo LawnSite Platinum Member
    Posts: 4,369

    Totally ignorant here but my understanding is the national electric code is 24in deep / 2in conduit. My beef is I lost a $23,000 install because of the cost of running the conduit. .....go by tonight and check site and other contractor has run 1in poly irrigation pipe and pulled it through ..... no there isnt going to be any irrigation.

    2x 20' pulls.
    he quoted $400 .........I quoted $1600+ materials using a directional boring guy.

    I talked to county ages ago and they were like you had to get it inspected etc etc. Could be fun.

    ps. Thanks for the reply guys.... i will take some photos tomorrow.
  5. Dirty Water

    Dirty Water LawnSite Fanatic
    Posts: 6,799

    Conduit size is not a national code.

    How deep is this poly pipe? I've seen poly used for conduit, it has a red stripe on it identifying that it is conduit and not water.

    I bet he will backfill the evidence without inspection, many fly-by-nights out here do that.
  6. stumpjumper

    stumpjumper LawnSite Member
    Posts: 183


    i'm a electrical contractor in oklahoma. the conduit size will be based off of the wire size, which will be based off of the load. all the information is in the nfpa code book. any high voltage installation(above 60 volts) in oklahoma has to be installed by a licensed electrician. 18 inches is the minimum for any high voltage underground. be careful, any injuries or damage and your legally responsible.
  7. mbella

    mbella LawnSite Bronze Member
    Posts: 1,284

    You lost a $23,000 install over $1200.00?
  8. kootoomootoo

    kootoomootoo LawnSite Platinum Member
    Posts: 4,369

    My bid was $23,000 and his bid was $26,000.......
    His bid after I had been awarded the job was $22,000.

    You know the young guy with all the fancy trucks, the pretty toys ...........the young guy who fails to mention daddy is a multi millionaire. but because he has pretty toys must know what he is doing.

    2 customers called me to tell me I had been awarded the contract because it was announced at the meeting. 2 weeks later he has the contract.

    As of friday I am pretty much booked out for the next 3 months now so its past caring but might let rich kid finish before I give pics to county.
  9. mbella

    mbella LawnSite Bronze Member
    Posts: 1,284

    HOA is all you had to say.
  10. olderthandirt

    olderthandirt LawnSite Platinum Member
    from here
    Posts: 4,900

    Need the name & # of the inspector to have the job inspected, if it's not to code it will be before they reopen the rd. that the inspector WILL close. :drinkup: