What the lighting world needs now........

Discussion in 'Landscape Lighting' started by MAGLIGHTING, Feb 8, 2009.

  1. djt22

    djt22 LawnSite Member
    from Ohio
    Messages: 113

    Spill I am not following your concern of the size of wire?
     
  2. Spilllight

    Spilllight LawnSite Member
    Messages: 32

    Connecting 10-12g LV wires to smaller gauge wires on the control device. Sometimes in the terminal connection there are several wires. Depending on the zone there could be more load than the control device can handle for a single "ON". Maybe I'm missing something.
     
  3. Lite4

    Lite4 LawnSite Gold Member
    Messages: 3,170

    you can only load up to 300 watts per zone. You shouldn't have ten wires for 300 watts. As long as you plan your zones accordingly you won't overload them.
     